Thanks for the help rockingit
Just for you information you can not normally run double insulated tails over long runs anyway even if they are RCD protected the DNO wont allow it, But good on you for admitting your mistake and sorting it outHi Just looking for some advice on meter tails in a flat.
The setup is 5 flats, i originally wired the meter tails in double insualted singles which was a mistake and am no in the process of rectifying it. Reasoning for calling it a mistake is the cable wont be rcd protected, for the majority of thier run they are in floor joists at a depth greater of 50mm but when they come up the wall to consumer unit they arn't. Reason for not rcd protecting is discrimination as if i put a 30ma RCD may be consumer unit that trips or Supply RCD which is in a service tunel. I could put a 100ma rcd but this wont comply as i understand as the cable are not buried at 50mm so either need mechanical protection or RCD. Hence i am now about to rewire in SWA. My question is i have already put in 16mm earth as well, so was planning on getting 2 core SWA and running this is to save wasting the 16mm earth. But just wanted to check i havent missed something i cant see why i cant leave the earth in place and use 2 core SWA for the supply?
Any replies would be great,
Thanks
Mark
Yeah, I use 8 loads myself, it's so easy to get hold of after all.
Hi Just looking for some advice on meter tails in a flat.
Reason for not rcd protecting is discrimination as if i put a 30ma RCD may be consumer unit that trips or Supply RCD which is in a service tunel. I could put a 100ma rcd but this wont comply as i understand as the cable are not buried at 50mm so either need mechanical protection or RCD.