Evening gents bit of advice, testing the above and when switches are on a reading of 3.13 ohms is apparent. Now when a switch is turned off I would expect a dead circuit I.e infinite >2000 but no a reading of 60.4 ohms is shown any thoughts on what this could be ?? Cheers
 
I suspect the 60 ohms is from the strapper thats not on as it were , the reading your getting is through the lamp ,
 
What about the other lamps on that circuit , because the feed to that 2 way circuit is common to the other lamps as well
 
  • Like
Reactions: 2 people
No not all other lamps were removed, so this could point to that but why would it show that is it reading all lamps on that circuit but why isn't it picking up on any other part of the circuit standard 1 way light either on or off. Is it due to the strappers cheers
 
No not all other lamps were removed, so this could point to that but why would it show that is it reading all lamps on that circuit but why isn't it picking up on any other part of the circuit standard 1 way light either on or off. Is it due to the strappers cheers

IMHO - no. both your reading are too high
 
Dave, if you're not doing the test proerly then you're A going to get daft readings and B wasting your time.
Go back and do it properly mate then if you're still getting silly readings then yell
 
The thing to be done on all lighting circuits is to remove all lamps and equipment like drivers , transformers , fans , shaver points etc to carry out the continuity and I/R testing , otherwise the readings are not going to be correct , because of the high readings your getting I would use the wandering lead method for R2 only and track down any loose connections that way as well ,,,
 
  • Like
Reactions: 4 people
Dave, if you're not doing the test proerly then you're A going to get daft readings and B wasting your time.
Go back and do it properly mate then if you're still getting silly readings then yell
Done it all twice and checked terminations 2 way light is end of circuit a junction before there is a reading of 0.84 but at the final light ( 3 spot lights on landing ) a reading of the above is shown I have tracked cables all IR tests fine just confused as to what it could be ?
 
Time for a daft question, is the circuit disconnected at the CU?
With the sudden jump in the readings I'd be thinking about a JB somewhere with dodgy connections. As Murdoch says, you should be able to have an educated guess at what the reading should be, give or take.
 
Connected in a connector block at ccu. Only 2 junction boxes on circuit both inspected and all terminations sound . This is a weird one all other r1 r2 test on this circuit gradually increased until the end of the circuit 2 way light
 
connected in a connector block at ccu. Only 2 junction boxes on circuit both inspected and all terminations sound . this is a weird one all other r1 r2 test on this circuit gradually increased until the end of the circuit 2 way light

wtf???
 
I would trace that cable from that fitting back to the last point , disconnect all the equipment etc as I already said and use a wandering lead method , and follow the circuit through , this way would be more accurate than R1 R2 method in that the fault could also be on the Live supply through possibly a faulty light switch if a junction box method is used ,

You could also apply this same wandering lead method on the Live as well if the fault lies there if required,,,
 
I would trace that cable from that fitting back to the last point , disconnect all the equipment etc as I already said and use a wandering lead method , and follow the circuit through , this way would be more accurate than R1 R2 method in that the fault could also be on the Live supply through possibly a faulty light switch if a junction box method is used ,
Faulty light switch could possibly be the one I will know more tomorrow when I go back. Will do as you say and hopefully find the fault!! Cheers
 
Faulty light switch could possibly be the one I will know more tomorrow when I go back. Will do as you say and hopefully find the fault!! Cheers

As I said earlier the 60 ohms is lamps still in , but the other reading is the one to be found and rectified ,,,
 
  • Like
Reactions: 1 person

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
r1+r2 test on 2 way lighting
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
28

Advert

Thread statistics

Created
Davem,
Last reply from
telectrix,
Replies
28
Views
3,365

Advert