Recent content by APElectrical

  1. A

    EICR LOCAL BONDING FLATS

    I’m sure this has been covered a squillion times before but advice please. EICR on block of 5 flats all with separate electrical supplies & meters. One boiler serving hot water via one system to all flats. Main bond to water and gas on entry to building. There is no bonding locally within the...
  2. A

    I’m sure this has been covered a squillion times before but advice please. EICR on block of 5...

    I’m sure this has been covered a squillion times before but advice please. EICR on block of 5 flats all with separate supplies & meters. One boiler serving hot water via one system to all flats. Main bond to water and gas on entry to building. There is no bonding locally within the flats...
  3. A

    Sunbed Supply

    I was planning on putting up a 63A vertical interlocked switched socket as there has to be a point of isolation locally outside the bed in case someone gets into trouble and sets the alarm off via a button inside the bed.
  4. A

    Sunbed Supply

    Perfect. Thanks for your time mate.
  5. A

    Sunbed Supply

    Sorry, have not installed the sunbed yet. Just quoting. The only specifications I have are from the client, direct from the manufacturer. That included needing a 63A supply, type C MCB and no 30mA RCD . The KW rating was not on the email. I have carried out work at the premises beforehand so...
  6. A

    Sunbed Supply

    Upright Sunbed. 63A supply in 16mm SWA 63A type C MCB to deal with initial inrush of current. 100mA RCD was recommended by manufacturer As 30mA Would cause nuisance tripping. Maximum earth fault loop impedance value for 63A type C MCB is 0.27. Ze is 0.21 How do I meet this value? Is there...
  7. A

    EICR MICC supplying shed socket. Buried in concrete but visible in many places along its...

    EICR MICC supplying shed socket. Buried in concrete but visible in many places along its length. MI non insulated. I say C2 but electrician I discussed this with thinks C3. Anyone else?
  8. A

    Boiler at end of bath

    The boiler has been in situ for a good few years and is serviced by British Gas every year. The landlord has said he is willing to box the boiler in.
  9. A

    Boiler at end of bath

    Moving consumer unit for first floor flat from a basement shop to locally within the flat itself via metal clad switch fuse at main intake. Had a quick look around at condition of the flats installation beforehand. Moved / upgraded con unit and was happily carrying out testing. Moved into...

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock