If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)
Evening all..

I am so used to the fact that there has to be Main bonding that I am struggling to not put it in in the following case:

Incoming pipe is plastic. The builder has then fitted a plastic stopcock (inside the house) and then a mixture of plastic and copper from there (see pic).

I haven't tested the copper pipe you can see next the stopcock but I expect it will test as connected to the MET due to parallel paths. It will be impossible to disconnect all these paths to see if extraneous.

I'm guessing with the new regulations I don't main bond? Plus it's plastic anyway, it would be ridiculous to put a clamp over plastic!

Bonding.jpg
 
They aren’t really new regulations regarding main bonding, they have just added a sentence detailing where main bonding may not be required for clarity.
As it has always been a requirement to bond extraneous conductive parts
 
When testing you are not checking if the conductive part is connected to the installation earth but whether it is connected to different potential from the earthing of the installation, in most cases this is the potential of the external ground.
Unless those copper pipes go down through the earth they are not introducing a different potential and so do not need bonding.
 
Evening all..

I am so used to the fact that there has to be Main bonding that I am struggling to not put it in in the following case:

Incoming pipe is plastic. The builder has then fitted a plastic stopcock (inside the house) and then a mixture of plastic and copper from there (see pic).

I haven't tested the copper pipe you can see next the stopcock but I expect it will test as connected to the MET due to parallel paths. It will be impossible to disconnect all these paths to see if extraneous.

I'm guessing with the new regulations I don't main bond? Plus it's plastic anyway, it would be ridiculous to put a clamp over plastic!

View attachment 44098
I would hazard a guess, that in the picture that is NOT the main water intake.
 
  • Like
Reactions: DPG
And there is a potential electrical outlet situated behind an appliance. :)
 
  • Agree
Reactions: Pete999
How do you work that out HHD
Because the builder installed it and he told me it was. He also explained how it was acceptable as a stop cock and explained why he actually preferred it to a standard metal tap (less likely to leak). It's his department and I except his word as a professional and competent builder.
 
I would agree with Pete, that looks like 15mm pushfit?
 
  • Like
Reactions: DPG and Pete999
Because the builder installed it and he told me it was. He also explained how it was acceptable as a stop cock and explained why he actually preferred it to a standard metal tap (less likely to leak). It's his department and I except his word as a professional and competent builder.
This Plumber that spun you that yarn, are you sure he is a Plumber?
 
Agree with Pete - doesn't look like main incomer. Looks like 15mm push fits. Unless he has adapted the incomer under the cupboard or floorboards.

Plus I don't like the stop tap just hanging there - bound to get knocked. There's a clip below it but the pipe isn't lined up with it. Very poor.
 
This Plumber that spun you that yarn, are you sure he is a Plumber?
Thanks for the input Pete, but I'll bow politely out of this conversation as it's the builders work not mine.
 
Never seen the water board send a bit of 15mm plastic in as a water main to be fair. Unless it's a holiday let being fed from an existing supply looks a bit strange.
 
  • Like
Reactions: DPG

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

HappyHippyDad

Esteemed
Arms
Supporter
~
Joined
Location
Gloucestershire
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Main bonding and the new regulations.
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
15

Advert

Thread statistics

Created
HappyHippyDad,
Last reply from
robd,
Replies
15
Views
5,312

Advert