It clearly does:
314.4 Where an installation comprises more than one final circuit, each final circuit shall be connected to a separate way in a distribution board
Not necessarily. A final radial circuit can be wired as a tree with multiple branches, one or more of which branches could be connected to the same way, so it is still only one radial circuit.
 
Not necessarily. A final radial circuit can be wired as a tree with multiple branches, one or more of which branches could be connected to the same way, so it is still only one radial circuit.
It clearly says that one radial (final circuit) needs its own way.
 
It clearly says that one radial (final circuit) needs its own way.
It's an argument as old as time, but my take is...

The interpretation of 314.4 is all down to how you define a final circuit.

If the regulation was meant to mean a final circuit will consist of a single line conductor in the case of a radial and two line conductors in the case of a ring, then this is what they should have said.

In my mind a final circuit is exactly what a competent electrician had designed it to be, accounting for design characteristics and manufacturers instructions. Therefore, as spurs are permitted, where and how the electrician decides to make a spur is not restricted by 314.4.
 
Doesn’t #40 answer your own question?

I agree with #43 above
 
It's an argument as old as time, but my take is...

The interpretation of 314.4 is all down to how you define a final circuit.

If the regulation was meant to mean a final circuit will consist of a single line conductor in the case of a radial and two line conductors in the case of a ring, then this is what they should have said.

In my mind a final circuit is exactly what a competent electrician had designed it to be, accounting for design characteristics and manufacturers instructions. Therefore, as spurs are permitted, where and how the electrician decides to make a spur is not restricted by 314.4.
There is no ambiguity in 314.4. The final circuits must have own RCBO or MCB.

A final circuit is any circuit whether it is a ring or radial, with any of them with branches, spurs, etc. It is clear in the writing of 314.4 they cannot be connected to one way.
 
There is no ambiguity in 314.4. The final circuits must have own RCBO or MCB.

A final circuit is any circuit whether it is a ring or radial, with any of them with branches, spurs, etc. It is clear in the writing of 314.4 they cannot be connected to one way.
but if you have 2 radials off 1 MCB, then those 2 radials combined are, by definition, 1 final circuit.
 
There is no ambiguity in 314.4. The final circuits must have own RCBO or MCB.

A final circuit is any circuit whether it is a ring or radial, with any of them with branches, spurs, etc. It is clear in the writing of 314.4 they cannot be connected to one way.
Maybe you're confusing cables with circuits.
A circuit can consist of more than one cable connected to the source.
 
There is no ambiguity in 314.4. The final circuits must have own RCBO or MCB.

A final circuit is any circuit whether it is a ring or radial, with any of them with branches, spurs, etc. It is clear in the writing of 314.4 they cannot be connected to one way.
You arguing a logical fallacy, an argument from authority.

You claim there is no ambiguity where the constant debates on this subject clearly reveal otherwise.

Rather than state, as fact, "there is no ambiguity" you should say "I see no ambiguity" which is fine, its a personal opinion and one your entitled to.

If you could add a technical reason why this practice is unacceptable then fine but at the moment the argument seems to me to be "I don't like it and the regs say you can't do it".
 
When I originally mentioned this reg on this post, I said this was fine and happens a lot, there is one reg to be mindful of, and asked the question - "can the two legs be considered one circuit".
The last bit is key, as very often they can, but sometimes they can't legitimately be classed as one circuit due to ccc or ocpd requirements.

For example, at a recent EICR I found an unlabelled 30 amp rewireable fuse, testing showed it fed a sub main to a shed and apparently strangely two sockets in a utility room. Take front off board and find a 6mm and a 2.5mm live in the same fuseholder. One might logically guess the 2.5mm was a radial for the two sockets. In fact it was yet another radial for a boiler FCU. (the utility room sockets turned out to be a joint box off the 6mm)
In that situation I had no issue citing 314.4 as one reason it wasn't adequate, the ocpd wasn't suitable for the boiler circuit and the whole lot was downright confusing. Definitely two circuits in the same fuseholder.

But if the same OCPD is needed, the same CCC, and the total loading is suitable, it clearly becomes one circuit in my mind.
 
You arguing a logical fallacy, an argument from authority.

You claim there is no ambiguity where the constant debates on this subject clearly reveal otherwise.

Rather than state, as fact, "there is no ambiguity" you should say "I see no ambiguity" which is fine, its a personal opinion and one your entitled to.

If you could add a technical reason why this practice is unacceptable then fine but at the moment the argument seems to me to be "I don't like it and the regs say you can't do it".
The text:
314.4 Where an installation comprises more than one final circuit, each final circuit shall be connected to a separate way in a distribution board

What don't you understand about the clear English 314.4 is written in?
 
When I originally mentioned this reg on this post, I said this was fine and happens a lot, there is one reg to be mindful of, and asked the question - "can the two legs be considered one circuit".
The last bit is key, as very often they can, but sometimes they can't legitimately be classed as one circuit due to ccc or ocpd requirements.

For example, at a recent EICR I found an unlabelled 30 amp rewireable fuse, testing showed it fed a sub main to a shed and apparently strangely two sockets in a utility room. Take front off board and find a 6mm and a 2.5mm live in the same fuseholder. One might logically guess the 2.5mm was a radial for the two sockets. In fact it was yet another radial for a boiler FCU. (the utility room sockets turned out to be a joint box off the 6mm)
In that situation I had no issue citing 314.4 as one reason it wasn't adequate, the ocpd wasn't suitable for the boiler circuit and the whole lot was downright confusing. Definitely two circuits in the same fuseholder.

But if the same OCPD is needed, the same CCC, and the total loading is suitable, it clearly becomes one circuit in my mind.
I don't see the difference.
 
This has been debated many times no harm in doing it again but can we keep it friendly.
 
The text:
314.4 Where an installation comprises more than one final circuit, each final circuit shall be connected to a separate way in a distribution board

What don't you understand about the clear English 314.4 is written in?
You're just shouting the same thing louder.

A final circuit, in my opinion, is any number of suitable conductors fed from the same OCPD.

Then you are into the realms of good workmanship and following manufacturers instruction.

A ten legged radial all in one MCB = crazy.

A two legged radial in one MCB = perfectly acceptable.

Any technical objections yet or are we sticking to the sophistry?
 
Don't put a SPD on to a RCBO, use a MCB if the SPD type demands some form of OCPD below the DNO's fuse rating (many larger SPD are fine up to 125A or similar fuses).
  • Firstly it is very likely to trip it on any modest surge event (as only 30mA equivalent to earth needed, averaged over the response time of the RCBO), disabling the SPD, and obviously taking out whatever other stuff the RCBO was feeding.
  • Secondly there is a grater chance of the RCBO electronics being damaged if it has to divert a 10kA or more spike, even if only for tens of microseconds.
 
The text:
314.4 Where an installation comprises more than one final circuit, each final circuit shall be connected to a separate way in a distribution board

What don't you understand about the clear English 314.4 is written in?
The crux of this lies in whether its acceptable to spur from the supply source of the final circuit to extend the circuit.
Consider this, would it be acceptable to spur off the circuit cable inside the CU using an appropriate junction connection?
 
  • Like
Reactions: dodger421
If it said each final circuit type must have it's own MCB it would probably make more sense, you wouldn't connect a socket or cooker circuit and a lighting circuit on the same MCB
 
  • Like
Reactions: dodger421
I believe the point is to specify the general configuration and function of a distribution board-based system rather than to define how many cables comprise each circuit. For example, it prohibits the 'tree system' where one main cable runs through every room in the house, with a fuseholder in each room tapping off that room's supply. This was popular in the early days of wiring. It also prohibits final circuits being paralleled up with distribution circuits and other random topologies.
 
I’ve just been in the BBB, looking at fig 15A and B, Spurs and fused spurs off ring and radial circuits. Although doesn’t mention 1.5mm on a 6A, but it does say……

725C9DB0-C4D6-42CA-ACFB-26D45706B611.jpeg
 
Weve been here before John. You've asked a question, received lots of good responses saying it's OK, and ow seem to want to argue the ---- using lots of bold writing and accusing people of not understanding English.
 
I’ve just been in the BBB, looking at fig 15A and B, Spurs and fused spurs off ring and radial circuits. Although doesn’t mention 1.5mm on a 6A, but it does say……

View attachment 86831

Absolutely, nothing wrong with that. Same circuit, just a spur.
 
  • Agree
Reactions: dodger421
Weve been here before John. You've asked a question, received lots of good responses saying it's OK, and ow seem to want to argue the ---- using lots of bold writing and accusing people of not understanding English.
I don't think it's okay?
 
Ah, fair point. Sorry.
Would you never connect a 2nd cable to the OCPD od a radial circuit then?
No your honour ?
 
The crux of this lies in whether its acceptable to spur from the supply source of the final circuit to extend the circuit.
Consider this, would it be acceptable to spur off the circuit cable inside the CU using an appropriate junction connection?
What you are saying is that two final circuits can be joined, with one being a spur or sub of the other. The spur point just happens to be at the source - the way. Sorry the text is clear on that. No ambiguity. I even underlined the words.
 
No opinions involved. The text is abundantly clear. I advise many to swot up on English.

I advise you speak to people with respect, rather than repeatedly asserting that your opinion is gospel and that other people don't understand English.

If you know the answer already then why ask the question? Or was it just to create an argument?
 
Weve been here before John. You've asked a question, received lots of good responses saying it's OK, and ow seem to want to argue the ---- using lots of bold writing and accusing people of not understanding English.
As a university graduate who had to extensively use and read English in studying and professionally all my life, I know simple English. I have written reams of technical documents and edited many others. It appears many cannot grasp something so fundamentally simple. Those who do not know English too well will ride along with the mob.

The text is abundantly clear - two final circuits cannot be connected to one way in and CU.
 
  • Disagree
Reactions: brianmoooore
We have two loads, A & B connected electrically in parallel to a DB way. The cables connecting them in parallel can run either [A-DB-B] or [DB-A-B]. The electrical implications of the two configurations are plain to see and don't seem to be in dispute. The argument is whether these two configurations have different textual descriptions, and therefore whether one of them is prohibited by a regulation.

In the meantime, people are connecting showers to RFCs, leaving CU busbar screws loose, running switch lines down the bare core of T+E, and being paid for it.
 
As a university graduate who had to extensively use and read English in studying and professionally all my life, I know simple English. I have written reams of technical documents and edited many others. It appears many cannot grasp something so fundamentally simple. Those who do not know English too well will ride along with the mob.

The text is abundantly clear - two final rings cannot be connected to one way in and CU.

Two final rings - yes I agree.

Is your argument not wandering off again though?

PS, I have a very good grasp of the English language, and have proof-read technical documents at a previous company. I don't always choose to use verbose language when typing forum posts on a mobile phone keypad however.
 
I advise you speak to people with respect, rather than repeatedly asserting that your opinion is gospel and that other people don't understand English.

If you know the answer already then why ask the question? Or was it just to create an argument?
I am being direct and open. I am not perfidious. Many here just cannot understand basic, simple English. They need to swot up. Simple.
 
  • Disagree
Reactions: brianmoooore
Ah, you've just edited your post 74 because I pointed something out.
 
Two final rings - yes I agree.

Is your argument not wandering off again though?

PS, I have a very good grasp of the English language, and have proof-read technical documents at a previous company. I don't always choose to use verbose language when typing forum posts on a mobile phone keypad however.
Circuit not ring. It says so in the text.

The text:
314.4 Where an installation comprises more than one final circuit, each final circuit shall be connected to a separate way in a distribution board

Point out what you do not understand.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Email
Joined
Time zone
Last seen

Thread Information

Title
two radials into an RCBO
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
94

Advert

Thread statistics

Created
John-SJW,
Last reply from
westward10,
Replies
94
Views
12,532

Advert