Engineer54
And our incomers were 3 pole with links. The reasoning being, switch the neutral and you remove one of the neutral earth paths. To break one of those links had to be a deliberate act.
There is the danger of closing the switch without the link fitted. But for the link to have been removed in the first place a responsible person would have authorised it and be accountable if not replaced.
The only time I’ve fitted 4 pole ACB’s was for stand by generators.
Sorry kid, we’re poles apart :yes:
Thanks for the kid quote, ....if only....lol!! :yes:
Now think about having Multiple 3 pole incomers from TX's and 3 pole bus couplers, all the TX neutrals commoned!!! How about having a faulty TX tripping out, but still having it's neutral being backfed even when it's out of service, well until someone actually goes and physically removes the neutral connection(s) anyway. ....So Yep, we sure are poles apart, all our switchboards are fully automatic both operationally and protection wise. When a supply needs to be fully isolated from the switchboard, we don't want to be messing around with a socket wrench or spanner to disconnect a neutral conductor, which in many cases could be several neutral conductors where parallel feeder supply's are involved!! No, i'll be definitely be sticking to the industry standard of 4 pole ACB's on main multi section switchboards. It's an absolute no brainer as far as i'm concerned...