Discuss 63 amp 3 phase socket protected by a 30 amp fuse RCD? in the Industrial Electricians' Talk area at ElectriciansForums.net

Flanders

-
Esteemed
Arms
Reaction score
965
Carrying out and EICR on large factory and they have welding plug into 63 amp commando sockets but are protected by 30 amp BS 88 fuses.

Now the regs states Socket outlets with a ratted current not exceeding 32 amp need RCD protection. 411.3.3 (i)

Because the Socket it 63 amp I say it does not need RCD protection because its the ratting of the socket that decides if an RCD is required ,not the over current protective device. So am not going to code this just put it as info on the observations.

Or would you guys Code it ?

Got me thinking though if you wanted to avoid fitting an RCD and don't what to do a risk assessment, just fit a 63 amp plug and socket and protected by a 16 amp MCB , Not sure how you would terminate the 1.5mm flex in the plug though :)
 
Just wondering why it is the ratting of the socket that is so important and not the ratting of the OCPD or have the boys and girls at the IET not thought of this ?
 
I’m also interested in this, we have a movable piece of equipment that is currently on a D16 with 16A MCB and 100mA RCD.
It trips the RCD (it’s in manufacturers documents that it needs a 300mA RCD).
Can I just change it to a 32A socket and remove the RCD?!
 
I’m also interested in this, we have a movable piece of equipment that is currently on a D16 with 16A MCB and 100mA RCD.
It trips the RCD (it’s in manufacturers documents that it needs a 300mA RCD).
Can I just change it to a 32A socket and remove the RCD?!

Why is it on a 100mA RCD if the instructions say a 300mA is needed?
 
I’m also interested in this, we have a movable piece of equipment that is currently on a D16 with 16A MCB and 100mA RCD.
It trips the RCD (it’s in manufacturers documents that it needs a 300mA RCD).
Can I just change it to a 32A socket and remove the RCD?!
No. A 32 amp socket will need a 30ma rcd protection if no risk assessment also as the manufacturers intructions say it needs a 300ma rcd then thats what you should fit, it could be triping the 100ma rcd as this is not suitable for your equipment, have you had the earth leakage tested or does it state in the intructions how much leakage there should be ?
 
It used to run fine on a 100mA RCD.
A mains filter was causing the problem, replaced it and problem went away but then came back. After speaking to manufacturer they said there can be 100mA of earth current (not that it needs 300mA, but I’ll fit one anyway).

Why does a 32A plug need an RCD, I too thought it was sockets of 16A and below?
 
Take a look in the 18th as it's all changed.
 

Reply to 63 amp 3 phase socket protected by a 30 amp fuse RCD? in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

Some advise or views would be appreciated. My supply is 100 amp single phase. I purchased my property 3 years ago or so, the owner prior to the...
Replies
29
Views
773
Hi everyone, I have been asked to pull in some new 3 phase supplies for 7 new welders which do not require a neutral connection. The client has...
Replies
4
Views
676
Hi all, Just a quick one regarding the need for RCD protection for socket outlets rated up to and including 32A. I have been tasked to install...
Replies
17
Views
1K
Hi guys, I am rewiring a commercial launderette with 3 phase machinery. Does the machinery need to be RCD protected being in commando sockets...
Replies
5
Views
4K
8.5K shower unit is wired to plastic box consumer unit to 30 amp cartridge fuse with no RCD It’s the original shower installed when the house was...
Replies
19
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock