Evening guys
currently got a bit of a pain in the azz ex collegue- use to work for the same company as me- now working for one of our clients- left on bad terms with our boss- and it seems he is trying to flex his muscles a bit- and is getting a little annoying now lol!
he over looks the eicr's that we do for his company and has the power to reject them and send back to us etc..
a few points I want some advise on:
I made a observations-
to which he replied:
I sort of agree/see his point- but If you can't visually see the sup bonding- but R<50V/Ia is met- then rcd is no required and sup bonding APPEARS to be present! what are your thoughts???
Also another one:
his comment...
as this is a eicr for a existing install- can't issue a c2 just because it isn't up to the current edition. Electrician testing to use his judgement right?
Thoughts???
currently got a bit of a pain in the azz ex collegue- use to work for the same company as me- now working for one of our clients- left on bad terms with our boss- and it seems he is trying to flex his muscles a bit- and is getting a little annoying now lol!
he over looks the eicr's that we do for his company and has the power to reject them and send back to us etc..
a few points I want some advise on:
I made a observations-
'Absence of RCD protection to circuits in a location containing a bath or shower, where supplementary bonding appears to be present. -C3'
to which he replied:
'The use of the word “appears” indicates that I could also not be there or not be complete, when it comes to Sup bonding or RCD protection it needs either or (ideally both) but if it doesn’t have RCD protection and only appears to have Sup bonding then this would raise a concern. It needs to be a statement of fact not allowing for any interpretation like we are trying to do now. To back this up The word “appears” leaves it open to doubt, Regulation 415.2.2 covers this and the R<50 V/Ia comes into play.'
I sort of agree/see his point- but If you can't visually see the sup bonding- but R<50V/Ia is met- then rcd is no required and sup bonding APPEARS to be present! what are your thoughts???
Also another one:
Absence of RCD protection to socket to be used by an un-skilled person (cooker switch socket)- unlike to be used for outside use- recommend protecting by RCD. -C3
his comment...
If the engineer can defiantly justify that this will not lead outside, for instance if its obstructed by a large item such as a fridge then I can understand a socket on the ground floor not being RCD protected. But unless this is only my interpretation current regs would pretty much rule out accessible (exceptions my point above for instance) socket outlet on the ground floor of not being applicable for the admittance of RCD protection. Regulation 411.3.3 only exempts labelled or identified for connection of a particular item of equipment. I wouldn’t have thought a cooker socket would come under this. Could this have not been played safe and RCD protected anyway to avoid doubts and future potential dangers?
as this is a eicr for a existing install- can't issue a c2 just because it isn't up to the current edition. Electrician testing to use his judgement right?
Thoughts???