scott 123

added sockets to existing ring worked all tests produced good results yet after 10 mins of power being on rcd trips cannot reset until ring neutrals are disconnected
 
Sounds like a N to E fault somewhere - and not necessarily on this socket circuit.

Some additional information might be useful - what did "all tests" consist of, and what actually were the test results that were "good". And a description of the board configuration would be helpful.
 
  • Like
Reactions: 1 person
As above more info required You could of trapped a neutral at one of the new socket or when you pulled the new cable in you could of burnt the cable against another one or there may be too many appliance now with high earth leakage on the circuit, did you get good IR results
 
As above more info required You could of trapped a neutral at one of the new socket or when you pulled the new cable in you could of burnt the cable against another one or there may be too many appliance now with high earth leakage on the circuit, did you get good IR results



end to end figure of eight IR >999
L 0.74 L cpc 51.2
N 0.74 N cpc 72.3
CPC 1.04
 
The way you have wrote the reading do not read correctly

I think you mean Ring reading

Live to live 0.74
Neutral to Neurtal 0.74
CPC to CPC 1.04

and IR test
IR >999 Live to live L cpc 51.2 and N cpc 72.3

Does the RCD test OK with nothing connected
 
I take it everything was unplugged for the test.

Has anything been plugged back in after?
 
Is there any load on the ring circuit ,
How have you installed the new cable ( if they are with other cables the could be burnt together when pulling them in) May be worth doing IR between the ring and other circuit if this is the case
Have you checked you have noted snaged a neutral when pushing sockets back
 
I take it everything was unplugged for the test.

Has anything been plugged back in after?

unplugged for test but soon after anything put on load on that circuit rcd trips
tried without sockets being pushed back still the same
 
Last edited by a moderator:
So either the appliance you have plug in has a high earth leakage coursing the RCD to trip or buy putting load on the circuit the insulation some were is braking down coursing the RCD to Trip
 
Sounds like neutral and earth conductors have been swapped at one of the sockets.
 
I would hazard a guess that as the RCD holds up when the N for the RFC is disconnected, and it was OK before, it's something you have caused, check from the points of addition.
 
Perhaps just the neutral in the wrong neutral bar of the CU. It does depend on whether it trips in tens minutes after power on or whether it trips at once when current is drawn.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
addition to ring
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
13

Advert

Thread statistics

Created
scott 123,
Last reply from
Richard Burns,
Replies
13
Views
1,703

Advert