Great return to work,managed to short circuit L & N on a brand new TPN db,took out mccb back in mains room.But completely ruined TPN DB,really surprised me,main switch blackened but ok when tested,but inner live rails giving poor IR results including neutral.Anyone else come across this.
 
complete accident when installing cable,it's a Schindler 12 way TPN DB,lots a black soot & smell of burning ,no visual sign of damage,but it does look a mess.Could it be the ionization of the fault causing the poor IR results,obviously conductive.
 
Something similar happened that I heard about recently. All new switch gear installed, new installation but alterations made before finally commissioned. Anyhow, not long after put into use, basically the whole thing blew up! Everything burnt out inc 400amp swicth gear. All the mcb's had black what looked like soot dust marks. it looked liked the whole installation had been struck by lightning. It would appear that an armoured cable shorted out within some metal stud work. But for whatever reason it messed up the whole installation.
 
We're all the switch gear replaced,thanks
 
Did it test okay before it was livened up? Testing after a short circuit will usually show low IR until all the insulators have been cleaned up or replaced.
 
complete accident when installing cable,it's a Schindler 12 way TPN DB,lots a black soot & smell of burning ,no visual sign of damage,but it does look a mess.Could it be the ionization of the fault causing the poor IR results,obviously conductive.

Who do you mean Schneider?
 
Yes sorry schineider
 
  • Like
Reactions: 1 person
The older Schneider DB's 3phase had exposed busbars at the rear of the main switch where it linked from the switch to the main carriage, a cover protected them at the front but anyone pushing cables behind would lead the risk of shorting out the phases with only the upstream OCPD to protect them, the risk is very high if you shove T&E behind before sleeving the earth, modern versions of the DB now have been designed so this cannot happen anymore. I've seen it done many yrs ago where the main switch turned into an electrical fire ball as the front end was the cutout which had been bodged.
 
The older Schneider DB's 3phase had exposed busbars at the rear of the main switch where it linked from the switch to the main carriage, a cover protected them at the front but anyone pushing cables behind would lead the risk of shorting out the phases with only the upstream OCPD to protect them, the risk is very high if you shove T&E behind before sleeving the earth, modern versions of the DB now have been designed so this cannot happen anymore. I've seen it done many yrs ago where the main switch turned into an electrical fire ball as the front end was the cutout which had been bodged.

Been there, done that, lost the eyebrows!
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

cliffed

Arms
~
Joined
Location
Worcester
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
Bang
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
13

Advert

Thread statistics

Created
cliffed,
Last reply from
davesparks,
Replies
13
Views
1,702

Advert