I'm doing testing ahead of a board change. It's a cramped Wylex rewirable installed by Spiderman himself. (I still haven't worked out why there seem to be 4 lives and 5 neutrals for lighting circuits, but that mystery will have to wait until the point of no return)
I eventually got the RFC lives and neutrals untangled and removed for an IR test. The cpc's are still connected unfortunately. L+N together to E at 250v is giving 8Mohms and slowly rising (reached 10 and still rising when I let go), but at 500v it's giving 0.5 Mohms.
Other than looking harder for connected equipment that I've missed is there anything this instantly suggests please?
I was suspecting outside lights on a FCU or something but can't see any.
(Zs is ok for all circuits. RFC continuity end to end is good too. Current main concern is this IR test result)
TIA
 
That sort of thing is common for SPD in something like an extension block, etc, but usually more extreme than that.

It would bother me as well if I could not find a reason, as the point of 500V testing is to uncover weaknesses in cables!
 
As above the CPC should be connected for this sort of test.

But if you see something dodgy, which you do, then try doing the test again but L+N to isolated CPCs. If much better then it really is a fault from cable to something else somewhere (i.e. leak to building via damaged sheath, not via cable's own CPC to connected equipment).
 
As above the CPC should be connected for this sort of test.

But if you see something dodgy, which you do, then try doing the test again but L+N to isolated CPCs. If much better then it really is a fault from cable to something else somewhere (i.e. leak to building via damaged sheath, not via cable's own CPC to connected equipment).
Cheers, I did a mind jump - I meant unfortunately I don't think I can get CPC's out as that was what my instinct said to do as well.
 
Firstly what a great bunch you are - didn't expect replies within 10 mins! Thanks all.
I've just found a USB charging socket that I missed and a bathroom mirror that looked innocent but turns out to have lights and a bluetooth speaker in it with a FCU behind it.
I've had to pack up for the night now but will be back tomorrow.
Thanks again.
 
Think I've found it. Single socket behind sofa with a surge protected extension lead in. Really should have noticed that but customer had assured me there were only two sockets in the lounge. She was quite excited to find this one!
Thanks again.
 

Reply to Interpreting IR test in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Just your thinking on this… Doing Remedials on a EICR … the DB is a old Wylex with MCB”S/RCD Its a 10 way… rammed packed with cabling,,,the...
Replies
3
Views
1K
Recently changed a CU for a friend and today when visiting one of the RFC's RCBOs tripped. It was due attention anyway as open ring and no time to...
Replies
13
Views
1K
Did a check on a ring circuit, due to board having to remain live I did it at a socket.. Was an RCBO, had checked RCD side and all tested ok...
Replies
3
Views
1K
Hi everyone, I'm nearly on my AM2 test and really enjoy the industrial side of things so I thought I'd learn by asking. I recently came across...
Replies
1
Views
754
M
Hi Guys I purchased some of the above online around 3 weeks ago, They are a fairly new product, very usefull as you can change both colour from...
Replies
1
Views
312

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock