N
NickD
I know this has been asked before but I can't locate a thread with a conclusive satisfactory answer...
Got an old Memera 3 board (says it's to BS5486 Pt.13) with a mix of BS1361 cartridge and BS3036 rewireables. PFC is 2.03kA. Breaking capacity of BS3036 may be 1/2/4kA depending on type (S1A/S2A/S4A), but I can't get any clarity on what the type means or how to tell what ones are present here so I have to assume 1kA. Upstream DNO fuse is stated as BS1361 60A type 2 which has 33kA breaking capacity (which I have no desire to rely upon).
So unless someone can tell me a way to honestly declare these BS3036s are S4As, I have an issue with breaking capacity < max PFC. However, I have a recollection of reading something somewhere which says that the breaking capacity can be that conveyed by the overall board enclosure rating, so does the board being BS5486 Pt.13 help me here? Can't locate it in BS7671 (and not sure it was in there anyway).
Advice much appreciated.
Hi Nick,
From memory, the problem that arises with 3036 rewirables is the time/current characteristics ( Appendix 3 ). Although the PSSC can be handled by the BS1361 Type 2 ( 33kA ), but as you say I wouldn't want to rely on this as the sole protection. No doubt there will be somebody on here who will be able to supply you with all the information, maybe Tony; I expect he invented them ( no malice intended ).
Regards.
Guidance note 3 says, on page 54, that you can take the s/c capacity of the fuses to be 16KA when:
the current ratings of the devices don't exceed 50A
The d/b is a 5486-13 or better
it is supplied through a type 2 BS1361 fuse rated at no more than 100A
I assume then that the BS 1361 will turn into a lump of glass after 2KA goes through it
Have you tried Eaton MEM technical? They did help me out with an enquiry about some old gear in the past, perhaps they still have specs on file somewhere? Alternatively, perhaps you could sidestep the issue by dropping HRC carriers and shields into the ways currently protected by rewireables?
YES!!!! That's the paragraph I remember. We must be on different versions of GN3 cos mine's on p.57 and says "Where a service cut-out containing a cartridge fuse to BS 88-3 (formerly BS1361) supplies a CU which complies with BS5486-13 or BSEN60439-3 Annex ZA, then the s/c capacity of the OCPDs within CUs may be taken to be 16kA".
I love you hillbillie, and I want to have your babies.
Considered it. It's not ideal having a mix (including at the same rating, 30A 3036s and 1361s both present and interchangeable - which have slightly different max Zs for 0.4 disconnection time, for a start, which is worrying, fortunately all relevant circuits have Zs well below the lower of the two figures) and rewireables are a potential nightmare anyway. Would cost the client about ÂŁ40 for used ones off eBay (which brings its own risk to me), doubt they'd go for it.
16ka is standard
Here's a link to a pdf by the IET supposedly relating to semi enclosed fuses / BS 3036...
https://www.google.co.uk/url?q=http://electrical.------.org/wiring-matters/29/semi-enclosed-fuses.cfm%3Ftype%3Dpdf&sa=U&ei=dEYtU-_CI6voywPGgoG4Cw&ved=0CCIQFjAA&sig2=TnIxjY1mi0EhsQ0KAODpKA&usg=AFQjCNHRHvxFL-kthByXPGNf_RRdm6oR4w
About as clear as mud when it comes to identifying the different duty cattogaries S1A to S4A
Reply to BS3036 Breaking Capacity in the UK Electrical Forum area at ElectriciansForums.net