I know this has been asked before but I can't locate a thread with a conclusive satisfactory answer...

Got an old Memera 3 board (says it's to BS5486 Pt.13) with a mix of BS1361 cartridge and BS3036 rewireables. PFC is 2.03kA. Breaking capacity of BS3036 may be 1/2/4kA depending on type (S1A/S2A/S4A), but I can't get any clarity on what the type means or how to tell what ones are present here so I have to assume 1kA. Upstream DNO fuse is stated as BS1361 60A type 2 which has 33kA breaking capacity (which I have no desire to rely upon).

So unless someone can tell me a way to honestly declare these BS3036s are S4As, I have an issue with breaking capacity < max PFC. However, I have a recollection of reading something somewhere which says that the breaking capacity can be that conveyed by the overall board enclosure rating, so does the board being BS5486 Pt.13 help me here? Can't locate it in BS7671 (and not sure it was in there anyway).

Advice much appreciated.
 
Hi Nick,

From memory, the problem that arises with 3036 rewirables is the time/current characteristics ( Appendix 3 ). Although the PSSC can be handled by the BS1361 Type 2 ( 33kA ), but as you say I wouldn't want to rely on this as the sole protection. No doubt there will be somebody on here who will be able to supply you with all the information, maybe Tony; I expect he invented them ( no malice intended ).

Regards.
 
Guidance note 3 says, on page 54, that you can take the s/c capacity of the fuses to be 16KA when:
the current ratings of the devices don't exceed 50A
The d/b is a 5486-13 or better
it is supplied through a type 2 BS1361 fuse rated at no more than 100A

I assume then that the BS 1361 will turn into a lump of glass after 2KA goes through it
 
Have you tried Eaton MEM technical? They did help me out with an enquiry about some old gear in the past, perhaps they still have specs on file somewhere? Alternatively, perhaps you could sidestep the issue by dropping HRC carriers and shields into the ways currently protected by rewireables?
 
Last edited:
Guidance note 3 says, on page 54, that you can take the s/c capacity of the fuses to be 16KA when:
the current ratings of the devices don't exceed 50A

YES!!!! That's the paragraph I remember. We must be on different versions of GN3 cos mine's on p.57 and says "Where a service cut-out containing a cartridge fuse to BS 88-3 (formerly BS1361) supplies a CU which complies with BS5486-13 or BSEN60439-3 Annex ZA, then the s/c capacity of the OCPDs within CUs may be taken to be 16kA".

I love you hillbillie, and I want to have your babies.
 
perhaps you could sidestep the issue by dropping HRC carriers and shields into the ways currently protected by rewireables?

Considered it. It's not ideal having a mix (including at the same rating, 30A 3036s and 1361s both present and interchangeable - which have slightly different max Zs for 0.4 disconnection time, for a start, which is worrying, fortunately all relevant circuits have Zs well below the lower of the two figures) and rewireables are a potential nightmare anyway. Would cost the client about £40 for used ones off eBay (which brings its own risk to me), doubt they'd go for it.
 
Funny how the onsite guide makes reference to a fuse (dno) that we can't actually open up and look at...

Snip, Snip - 'I saw no seal' ;)
 
Ridiculous isn't it? You potentially can't complete an EIC or EICR without knowledge of the DNO cutout fuse type/rating, but legally you can't pull it to see.
 
I know this has been asked before but I can't locate a thread with a conclusive satisfactory answer...

Got an old Memera 3 board (says it's to BS5486 Pt.13) with a mix of BS1361 cartridge and BS3036 rewireables. PFC is 2.03kA. Breaking capacity of BS3036 may be 1/2/4kA depending on type (S1A/S2A/S4A), but I can't get any clarity on what the type means or how to tell what ones are present here so I have to assume 1kA. Upstream DNO fuse is stated as BS1361 60A type 2 which has 33kA breaking capacity (which I have no desire to rely upon).

So unless someone can tell me a way to honestly declare these BS3036s are S4As, I have an issue with breaking capacity < max PFC. However, I have a recollection of reading something somewhere which says that the breaking capacity can be that conveyed by the overall board enclosure rating, so does the board being BS5486 Pt.13 help me here? Can't locate it in BS7671 (and not sure it was in there anyway).

Advice much appreciated.
16ka is standard
 
Here's a link to a pdf by the IET supposedly relating to semi enclosed fuses / BS 3036...

https://www.google.co.uk/url?q=http://electrical.------.org/wiring-matters/29/semi-enclosed-fuses.cfm%3Ftype%3Dpdf&sa=U&ei=dEYtU-_CI6voywPGgoG4Cw&ved=0CCIQFjAA&sig2=TnIxjY1mi0EhsQ0KAODpKA&usg=AFQjCNHRHvxFL-kthByXPGNf_RRdm6oR4w


About as clear as mud when it comes to identifying the different duty cattogaries S1A to S4A
 

Reply to BS3036 Breaking Capacity in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock