Can an MCB be used instead of an RCBO for a supply to a UPS centeral battery system if the required disconnection times are met?
 
Don't see why not
 
Upvote 0
As a matter of interest, what sort of size is this central battery system?? At what point in the that system are you intending to replace the existing RCBO??
 
Upvote 0
If my memory serves me right, it is a 6kVA system that is installed. (by a different company)

Originally I was told by my boss that a 50A supply was needed to the comms room. I installed a 16mm cable protected by a 50A 30mA RCBO.

The engineer who installed the system has now requested that a 32A MCB be put in place of the RCBO as there will be a high earth leakage which may trip the 30mA RCBO.
 
Upvote 0
Further thinking on this - if the earth current is over 30mA, what does the Designer say about the Installation? Surely there is a standard design for these installations?
Now that you know it could be over 10mA earth current, then you need to read 543.7.
 
Upvote 0
The cable is run on tray above a suspended ceiling. It is a 16mm 3 core hi-tuf cable. Single phase. I haven't been speaking to the designer yet. Should see him on Monday.
 
Upvote 0

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Advert

Thread statistics

Created
Hawk,
Last reply from
Hawk,
Replies
7
Views
1,250

Advert