G
Guest55
BTW Biff 35mm²Al/Cu is the usual now.
not for 100A single phase it isnt.
not unless the nearest mains is 100 or more yards away.
BTW Biff 35mm²Al/Cu is the usual now.
No, around here, which is WPD, it's definitely 16mm Al with Cu spiral. I've got some, and I've also had to work with it on DNO kit that's transferred to private (don't ask).
No, around here, which is WPD, it's definitely 16mm Al with Cu spiral. I've got some, and I've also had to work with it on DNO kit that's transferred to private (don't ask).
It could be 400A fuses in the sub station "protecting the cable" The assumption is the service cable will burn open circuit in the event of a fault. Substation fuses do not protect cables they are there to grade with the HV protection for the local TX.Well i wouldn't feel happy with a 16mm Ally concentric or split concentric cable with a 100A BS 88 protecting it. A 60A fuse i probably wouldn't be too phased about!! lol!!
The cutout fuse provides overcurrent protection
It could be 400A fuses in the sub station "protecting the cable" The assumption is the service cable will burn open circuit in the event of a fault. Substation fuses do not protect cables they are there to grade with the HV protection for the local TX.
For the installation not the service cable.
Agree, i am aware of the philosophy behind the DNO LV fuse grading with the MV protection of local TX subs. But i still wouldn't be happy with a 16mm AU conductor supplying 100A service fuse. But then i wouldn't use AU cables at any level!! lol!!
I thought it did for the service cable?
That picture is weird when you scroll up and down, it looks like it is coming out the page!The OCPD is back at the substation or feeder pillar. Anything up to 630A so as meclec said, the service cable should blow clear. It’s a bugger when it doesn’t and the breach joint blows.
The sphincter is twitching when you put one of the old “J” type feeder fuses in live. The new SAIF pillars are a doddle to work on live.
This is a SAIF pillar