It is quite easy to install 4kWp installations and get within even the strictest DNO requirements, you know, the mad ones stating 3.68kW. Always state on the G83 form that the maximum generation ability is not greater than 16A.
This can be verified on the following basis.
Maximum DC generation capacity is 4kWp
Efficiency of inverter eg 95 %
Supply voltage = 243V
Make the calculation and the maximum generation capacity of the SSEG is (4000x0.95)/243 = 15.638A