Probably going to get slated for not knowing/doing something wrong but here goes!!

So, been asked to do a board change for a customer, when I turned up they explained that had had a new PME done a few weeks ago, when I mentioned that their house wasn't earthed the customer said that the installers had said it 'wasn't urgent but needed doing at some point' . Anyway I did a quick ZS test on a socket and found I was getting 1.20 ohms..not bad for no earth.

I then proceeded to start dead testing the existing board, upon testing a ring circuit in the house I found that I was getting voltage (190v) between the disconnected neutrals and live. At 1 point I even had the neutral tail disconnected from the meter with the ring neutrals connected on to the neutral block to find all the electrics working in the house!! (To try and explain to the customer what is happening)

Any suggestions on where I begin to start looking for this fault??

Cheers in advance
 
i'd start by sorting out the earth -- diss. all bonding then once you have a decent earth, proceed logically. ( my grandmother was a Vulcan).
 
I then proceeded to start dead testing the existing board, upon testing a ring circuit in the house I found that I was getting voltage (190v) between the disconnected neutrals and live.
Hi - this has me confused - are you saying the double pole isolation switch in the board was off and yet you were reading 190V?
 
Hi - this has me confused - are you saying the double pole isolation switch in the board was off and yet you were reading 190V?
No, the 2 neutrals of my ring circuit were disconnected and I was reading 190v between each leg and incoming live.
[automerge]1571767195[/automerge]
Hi - this has me confused - are you saying the double pole isolation switch in the board was off and yet you were reading 190V?
...and yes I had it live with the cover off if that's what you are referring to.
 
Last edited:
No, the 2 neutrals of my ring circuit were disconnected and I was reading 190v between each leg and incoming live.
I'd expect that :rolleyes: Were you using a multimeter by any chance ?
There's capacitance between the neutrals and earth, as well as possibly some conductance (inverse or resistance). You've formed a potential divider between L & E with your meter as one leg, and the N-E impedance as the other leg. The voltage (and phase) of the midpoint (the N wires) depends on the ratio of the impedances of your meter and N-E.
 
Hi,could i ask what detailed inspection and testing,was done,regarding the earthing arrangements,at origin?

I'd expect that :rolleyes: Were you using a multimeter by any chance ?
There's capacitance between the neutrals and earth, as well as possibly some conductance (inverse or resistance). You've formed a potential divider between L & E with your meter as one leg, and the N-E impedance as the other leg. The voltage (and phase) of the midpoint (the N wires) depends on the ratio of the impedances of your meter and N-E.
How does this explain disconnecting the neutral tail coming out of the meter and the board still being live across L-N? And no not using multimeter, checked it with both my multifunction tester and voltage testers.
 
I don't understand your initial question. You know you've got an N-E fault(s), you demonstrated it to yourself and the customer. You also have suspect earthing conductor connectivity or similar. The two don't sit nicely together - they can make lots of exposed stuff live.

As per Fairlight, start testing from the beginning, systematically, in order. Make no assumptions, take no guesses. When you find the circuit with the N-E fault, check it carefully for thermal damage. Your disconnected neutral tail would have sent the entire load current of the house down it, and if it's a lighting circuit... 1mm isn't really specced for that!
 
Hi,i'll be honest,if i was attempting to explain a situation to a customer,in a property with a suspected earth issue,disconnecting the neutral tail,and leaving the line connected,would not be a method i would choose.

This is a situation,which would be considered dangerous,in an older property,where earths at origin,may be poor,and an original fused neutral,had blown.
 
Hi,i'll be honest,if i was attempting to explain a situation to a customer,in a property with a suspected earth issue,disconnecting the neutral tail,and leaving the line connected,would not be a method i would choose.

This is a situation,which would be considered dangerous,in an older property,where earths at origin,may be poor,and an original fused neutral,had blown.
Any good advice to give, you have taken the time to post 3 times on this topic but every post is irrelevant to the question I asked?
 
Any good advice to give, you have taken the time to post 3 times on this topic but every post is irrelevant to the question I asked?

I too do not like irrelevant or negative coments when asking a legitimate question, but I think you need to re read pegs posts as they are relevant and I couldn’t detect any negativity other than stating concern over a potentially dangerous issue.

In the past we have had on this forum, if you don’t know you shouldn’t be doing it. It’s changed.

all the posts have been in order to help. Re read them.
 
Any good advice to give, you have taken the time to post 3 times on this topic but every post is irrelevant to the question I asked?

The best advice I'd give to start with is that you stop creating dangerous situations by disconnecting the neutral of a live installation.
As lucian has pointed out this will have diverted the load current via the fault to earth and potentially caused a lot of damage in doing so, not to mention the significant danger to your life and that of anyone else in the property.
 
How does this explain disconnecting the neutral tail coming out of the meter and the board still being live across L-N?
Oh dear. You need to read it again.
You've made no mention of isolating the incoming L so we have to assume that's at around 240V relative to earth and incoming N.
You've disconnected the N.
You measure between the 240V L and something that is now "sort of floating" with various resistive and capacitative paths (one of which is your meter) to both L and E.
So the N will be at some voltage between E and L - and you are measuring the difference between that and L.
 
This thread is making my head hurt. I've read it start to finish and back to front. Still can't work out what the heck is going on
 
Hi dude,i apologise if i have offended you,but your original post title,was regarding the earthing. You were asked several times,including by myself,regarding this,and got no answer.

I am sorry you think my points regarding the safety aspect of disconnecting and then demonstrating,are irrelevant....this is a worry.

I wish you well and success in your quest,but as the great Deborah Meaden said....i'm out?
 

Reply to Earth/Neutral fault..Help Needed!! in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
445
Hello, I'm not an electrician, more one of those 'competent DIYers', so probably the worst kind :) My electric shower broke, the shower firm came...
Replies
13
Views
1K
Hi was recently at a property and was installing a Solar PV system. was doing my testing and i came across a weird result when doing the...
Replies
23
Views
3K
Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
624

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock