TT system Ze is 17.5 ohms but when connected it is 0.60 ohms? Have one outgoing 95mm SWA and one 240mm SWA earthed either end and individual rods?
Thanks
 
parallel paths via bonding and/or the other rods.
 
What is the means of earth fault protection to the SWA's?
Has a main adjustable RCD
[automerge]1579416233[/automerge]
It’s an overhead 3 phase supply, looking at the electric board cut out there’s no earth there eg TNS or PME, but at the other end of the tails connected to a DB there’s an earth there, tested that at 17.5 ohms and connected in parallel with all other DBs and it’s 0.60 ohms, then my highest sub circuit is about 1.57 ohms
 
Just a thought, is the earth into the DB of sufficient section?
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
London
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Earth readings
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
4

Advert

Thread statistics

Created
Bradley6969,
Last reply from
Mike Johnson,
Replies
4
Views
1,619

Advert