Hi all,
Thank you in advance...
So I had an electrician put in some FCUs on spurs to a couple of outside lights.. this one was in readiness to feed a pond pump.

I'm very reluctant to question the experts, but I wanted to put an LED FCU on, and found this.. I really don't think it can be right?

Surely both cables going into the supply bypasses the fuse?

Am I missing something?

Again, I appreciate any advice..
FCU wiring.jpg
ù
 
Last edited by a moderator:
If the load is connected then the fuse is bypassed, but I can't help wondering if no load has yet been connected and those cables are simply the supply looped through to another point as the cables look to be the same size of T&E of different ages..
 
  • Like
Reactions: Dave64 and DPG
If the load is connected then the fuse is bypassed, but I can't help wondering if no load has yet been connected and those cables are simply the supply looped through to another point as the cables look to be the same size of T&E of different ages..
The way I read it, it's been put in ready for the pond feed so the cables are just both legs of the ring. The pond feed will go into the load side.
 
  • Like
Reactions: DPG and nicebutdim
The way I read it, it's been put in ready for the pond feed so the cables are just both legs of the ring. The pond feed will go into the load side.
That was my take, but wasn't certain I'd picked the OP up correctly.
 
Yes, no load connected.. and probably another case of "competent DIYer" not being completely competent..
Thank you all..
 
How do I connect my pump?
 
That was my take, but wasn't certain I'd picked the OP up correctly.
Hi, thank you for your reply. This FCU is spurred off of the ring, one cable goes to a double socket on the ring, and the second cable goes through the wall to an external junction box and ends in a cable connector. Into which, the electrician said I could connect my pump with armoured cable.
 
Hi, thank you for your reply. This FCU is spurred off of the ring, one cable goes to a double socket on the ring, and the second cable goes through the wall to an external junction box and ends in a cable connector. Into which, the electrician said I could connect my pump with armoured cable.

Something isn't right here and I would advise against connecting anything without first getting someone in to look at it.
 
  • Like
Reactions: DPG
Hi, thank you for your reply. This FCU is spurred off of the ring, one cable goes to a double socket on the ring, and the second cable goes through the wall to an external junction box and ends in a cable connector. Into which, the electrician said I could connect my pump with armoured cable.
If thats the case then the cable that goes through the wall to the jb should be on the Load side so you can isolate it,
 
  • Like
Reactions: Dave64
Something isn't right here and I would advise against connecting anything without first getting someone in to look at it.
I agree. I have three of these FCUs each spurred from a different socket. One to some brick lights, one to decking lights and the third in readiness for the pond pump.
I've simply changed the FCUs to ones with LEDs.. The brick and decking lights work fine, but the pump one didn't seem right.
And given that these electrics are repairs to a conservatory after a fire caused by electrics, I am extra cautious.
 
Doesn't seem like a mistake any electrician would make, though.
I agree. But they have replaced all the electrics in the conservatory.
 
Thank you all who replied.
I will contact the contractors and ask them to check the wiring.
 
  • Like
Reactions: DPG and nicebutdim
Finally found out what was going on here, a bad case of "competent DIYer" not really being all that competent..
It turns out that the two cables into the supply were simply the supply and the loop to the next FCU... the load cable was taped up at the back of the box!
Hats off to all you pros... firstly, for be good at electrics, and secondly, for putting up with muppets like me! And I joke, but I genuinely realise how dangerous electricity can be !!
Thanks for reading, and thank you for a great forum!
 
I know.. I'm humbled! And safe!
 
  • Like
Reactions: nicebutdim
Every day is a learning day for me. I doubt your days are any different.
Indeed, the same electrician also made me realise you shouldn't have two RCDs in the same circuit!!
Respect to the trades.... !
 
  • Like
Reactions: nicebutdim

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
chesterfield
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
DIY or Homeowner (Perhaps seeking pro advice, or an electrician)

Thread Information

Title
FCU to pond pump
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
17

Advert

Thread statistics

Created
Dave64,
Last reply from
Dave64,
Replies
17
Views
1,588

Advert