Installing a 13K peak (10K running) generator 190 feet from the panel. The portable generator is housed in a shed at the end of the property. What gauge wire and breaker amperage is required? Getting mixed information. Differing voltage drop calculators and breaker suggestions have me confused and vary from 30 to 60 amp breakers and between 4 and 6 gauge wire. Anything else I need to be aware of in this setup?
 
I presume you mean 13kva
what voltage is the generator?
 
I presume you mean 13kva
what voltage is the generator?
Thanks for the quick response. 13,000 Watts peak, 10,000 watt running. Its a DuroMax portable.
 
Installing a 13K peak (10K running) generator 190 feet from the panel. The portable generator is housed in a shed at the end of the property. What gauge wire and breaker amperage is required? Getting mixed information. Differing voltage drop calculators and breaker suggestions have me confused and vary from 30 to 60 amp breakers and between 4 and 6 gauge wire. Anything else I need to be aware of in this setup?
Your generator is going to dictate how big the wire needs. I’m going to assume that you have a 50 amp receptacle on the generator so having said that you will need # 6 wire with 4 conductors in it. If it’s going to your panel then you would need a 50 amp breaker. A picture of your generator would be nice.
 
  • Like
Reactions: James
Your generator is going to dictate how big the wire needs. I’m going to assume that you have a 50 amp receptacle on the generator so having said that you will need # 6 wire with 4 conductors in it. If it’s going to your panel then you would need a 50 amp breaker. A picture of your generator would be nice.

1654706761328.png



Thanks again for your time and knowledge.

Below the picture is the Amazon link.

So, don't need to go to 4 gauge? That is my main concern since it is a 190 foot run from the generator to the panel.
 
As an Amazon Associate we earn from qualifying purchases.
As an Amazon Associate we earn from qualifying purchases.

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Leonia, NJ
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United States of America
What type of forum member are you?
Other

Thread Information

Title
For a 13K peak (10K running) generator, what gauge wire and breaker amperage is required?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
6

Advert

Thread statistics

Created
lepersrepel,
Last reply from
Megawatt,
Replies
6
Views
6,426

Advert