wml5275

DIY
Reaction score
0
I plan to upgrade my portable generator to a larger 40 amp max output unit.

When I originally ran the cable to my electrical panel I used 8/3 NM-B W/G wire to allow for a future upgrade.

My question is what gauge SOOW should I use for the 10 foot generator lead, 8/4 or 6/4? I'm a little confused as to why 8/3 NM-B is rated for 40 amps and 8/4 SOOW is rated for 30 amps?

Any information would be appreciated.

Thanks to all
 
Different types of cables have different current ratings for the same size conductor because the different types of insulation can handle different temperatures.
The conductors warm up during use and current ratings, when you get down to basics, are just telling you how much current a cable can carry before it gets too hot.

Some cables such as flexible cables will have lower current ratings because they are expected to be touched/handled whilst in use and so the surface temperature needs to be lower.
 
I plan to upgrade my portable generator to a larger 40 amp max output unit.

When I originally ran the cable to my electrical panel I used 8/3 NM-B W/G wire to allow for a future upgrade.

My question is what gauge SOOW should I use for the 10 foot generator lead, 8/4 or 6/4? I'm a little confused as to why 8/3 NM-B is rated for 40 amps and 8/4 SOOW is rated for 30 amps?

Any information would be appreciated.

Thanks to all
Wm welcome to the forum and why are You using SOOW wire, you can get 8/3 with ground Romex. Its good for 50 amps and it’s approved for underground and wet locations. You can go to Lowe’s or Home Depot and purchase it by the foot. Are you saying that you are going to change the 30 amp plug on the generator to a 40 amp plug. What’s the wattage of your generator ? Romex is NMS cable and who told you it’s just good for 40 amps ?
 
Thank you.

As I mentioned in my post the main cable that I ran to my electrical panel is
8/3 NM-B W/G wire. I'm only using 10' of the SOOW cable to run from the inlet box to the generator because the 8/3 is not as flexible as the SOOW.

The new generator is 10,000 running watts rated 240 volts 40 amps and has a 50 Amp, 125/250 Volt Nema 14-50 3-Pole/4-Wire receptacle.

With regard to the 40 amp rating for the 8/3 that is what is listed on the Home Depot website for that particular wire. https://www.homedepot.com/p/Southwi...x-SIMpull-CU-NM-B-W-G-Wire-63949299/204632779

I was just asking if I should use the 8/4 SOOW or 6/4 SOOW for the 10' lead?
 
Thank you.

As I mentioned in my post the main cable that I ran to my electrical panel is
8/3 NM-B W/G wire. I'm only using 10' of the SOOW cable to run from the inlet box to the generator because the 8/3 is not as flexible as the SOOW.

The new generator is 10,000 running watts rated 240 volts 40 amps and has a 50 Amp, 125/250 Volt Nema 14-50 3-Pole/4-Wire receptacle.

With regard to the 40 amp rating for the 8/3 that is what is listed on the Home Depot website for that particular wire. https://www.homedepot.com/p/Southwi...x-SIMpull-CU-NM-B-W-G-Wire-63949299/204632779

I was just asking if I should use the 8/4 SOOW or 6/4 SOOW for the 10' lead?
WM just buy the # 6 then you will for sure be OK. I don’t care what they’re website tells you if you had a copy of the 2020 NEC code book it has and article just for cables, cords and their amperages. Good luck
[automerge]1581210123[/automerge]
Thank you.

As I mentioned in my post the main cable that I ran to my electrical panel is
8/3 NM-B W/G wire. I'm only using 10' of the SOOW cable to run from the inlet box to the generator because the 8/3 is not as flexible as the SOOW.

The new generator is 10,000 running watts rated 240 volts 40 amps and has a 50 Amp, 125/250 Volt Nema 14-50 3-Pole/4-Wire receptacle.

With regard to the 40 amp rating for the 8/3 that is what is listed on the Home Depot website for that particular wire. https://www.homedepot.com/p/Southwi...x-SIMpull-CU-NM-B-W-G-Wire-63949299/204632779

I was just asking if I should use the 8/4 SOOW or 6/4 SOOW for the 10' lead?

I personally would not use SOOW cord but it’s your choice. I’m trying to help but you seem to have it figured out
 
WM just buy the # 6 then you will for sure be OK. I don’t care what they’re website tells you if you had a copy of the 2020 NEC code book it has and article just for cables, cords and their amperages. Good luck
[automerge]1581210123[/automerge]


I personally would not use SOOW cord but it’s your choice. I’m trying to help but you seem to have it figured out
I'm curious as to why you would not use SOOW?
 

Reply to Proper SOOW wire gauge in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I thought that I posted this in the DIY part of the forum but I believe I did not. I am sorry about that. I put in a 10' x 20' metal shed about...
Replies
2
Views
1K
Installing a 13K peak (10K running) generator 190 feet from the panel. The portable generator is housed in a shed at the end of the property...
Replies
6
Views
3K
I’m running wires to the basement for future basement finishing. I’d like to add two circuits of outlets (one on the finished side and one on the...
Replies
0
Views
581
I would like to ask advice on a breaker size. Back in 2001 I turned my garage into a woodworking shop with several 240v machines. To power them I...
Replies
2
Views
1K
Ok so live in 89 mobile home ugh I really need lots of work but I'm on disability and I cannot afford electrician but I've been working with all...
Replies
1
Views
808

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock