Sorry guys yes the fuse board in the garage is plastic.
Tony- what was at the pub or college (or collage as you say, I assume you mean college)
If you mean the part about earthing at one end. Yes I have been informed by many people including an earlier post here that's its acceptable to earth only at one end. Secondly it was a college lecturer that told me it should be earthed at both ends. If you insist on knowing more details just in case I have not convinced you enough yet it was during the 2391-20 design, erection and verification course in Rotheram with Connaught electrical when they were around. Think the lecturer was called Dave and we had ham sandwiches for lunch. No beer was allowed so it certainly wasn't in the pub. Convinced now?[/QUOTE
the armour of the SWA must be earthed. if it is not used as a cpc, then it only needs earthing at 1 end. if used as a cpc, then both ends need to be earthed. hope that clarifies it.