Alextrician

So I’ve finished a rewire recently and I’ve come to testing the ring circuit for the down stairs sockets and I’m not getting what I’m testing in regards to the calculation

LL: 0.36
NN:0.36
EE:0.60(there abouts)

Now when I’m doing the r1+r2 crossing the opposite live and earths but the calculation for obtaining it isn’t what I’m getting when recording the results.

So 0.36+0.36/4= 0.18

But when testing at the sockets I’m getting readings of 0.30 ohms. I’m going to try another calibrated tester this weekend.


Any advice would be appreciated

Thanks
 
It its a R1+R2 when doing the “figure of 8” on a RFC. Are you testing at the terminals of the socket or are you testing with a socket tester through the socket itself?
 
  • Funny
Reactions: gazdkw82
It its a R1+R2 when doing the “figure of 8” on a RFC. Are you testing at the terminals of the socket or are you testing with a socket tester through the socket itself?
I did both I took all the fronts off and tested at the terminals and also went round with a socket tester.
 
Are you testing at the back of the socket or using a socket tester adapter?

Check all terminations

Have you zero'd before every test?

Your allow 0.05 above and below your calculated reading (0.18)
 
Are you testing at the back of the socket or using a socket tester adapter?

Check all terminations

Have you zero'd before every test?

Your allow 0.05 above and below your calculated reading (0.18)
Both mate nulled the leads more than one and still to no avail. Going to have to strip determinate and re test and see how things go
 
As per Doc I would say your reading is correct allowing for poor contact.
 
Dirty or unused sockets can give odd readings ...

But you are calculating it wrong ....

0.36 + 0.60 = 0.96 / 4 = 0.24
Thought it was. Watched a video because I got confused and that’s how he did it should’ve looked in the onsite guide
 
Dirty or unused sockets can give odd readings ...

But you are calculating it wrong ....

0.36 + 0.60 = 0.96 / 4 = 0.24

Spot on. I didn't read the post very well
 
LL: 0.36
NN:0.36
EE:0.60(there abouts)

Now when I’m doing the r1+r2 crossing the opposite live and earths but the calculation for obtaining it isn’t what I’m getting when recording the results.

So 0.36+0.36/4= 0.18

But when testing at the sockets I’m getting readings of 0.30 ohms. I’m going to try another calibrated tester this weekend.


Hi,

I've noticed your figures your using are wrong. You say R1+R2 but have used R1 & Rn figures

Should be 0.36 + 0.6 / 4 = 0.24

Then your allowed the 0.05 tolerance


Edit

Beaten by Murdoch
 
You skip all the other posts :p
 
Alextrician is a good one I like it
 
Still isn't righr. Check terminations, check tester has sufficient battery, check you've zero'd properly.
 
I’d hazard a guess you might have nipped some insulation somewhere giving you a slightly higher resistance.
 
  • Like
Reactions: Wilko
Your talking about 0.06 ohms from the calculated rule of thumb.

Its really not a big deal.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Help or advice with r1+r2 ring.
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
27

Advert

Thread statistics

Created
Alextrician,
Last reply from
Pete999,
Replies
27
Views
3,829

Advert