ESQCR doesn't actually specify any max Ze values, the values are broad targets from an 'engineering agreement'.

Amazingly, there is no 'regulation' to force a DNO to comply with the 'engineering agreement' values!
 
I cant actually believe this, the ESQCR requires the DNO to maintain the Ze below the maximum of 0.35 for 100a TN-C-S system if they are supply the earth facility

ESQCR mentions no max figures for tncs

This can not be acceptable as a permanent solution, if it was my job I would kick up a fuss about it and if nothing was done have their rcd removed and fit an s type 100ma as my main switch

Not too much you can do about, you could TT it.

Is it an S type RCD? they have fitted?
If not why bother to fit the 17th edition split ccu`s as there is now no dicrimination with the supply
Are they going to pop around once a quarter and press the test button on their rcd

The ESQCR requires equipment of the dno and suppliers to ensure their equipments meets BS 7671, so an s type would ensure this.
If you have a 100 fuse and your ZE is 0.55 ohms this may be down to network parameters, but this wouldn't comply with BS7671, so they stick an rcd in to comply
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
High Ze - DNO added an RCD!
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
22

Thread Tags

Advert

Thread statistics

Created
Kevin,
Last reply from
Chr!s,
Replies
22
Views
7,913

Advert