Have you checked insulation resistance?
 
Is the RCBO on or off? Are other circuits with nearby cables energised? It's an unusual reading to take, because it doesn't tell you anything very useful. what prompted you to connect the line and neutral but not the earth, and then measure the voltage from that to the bar?
 
Funnily enough I had something a bit similar today (though lower voltage).

During a CU change there were 3 sets of T+E in a B32 device. I wanted to check it was two for an RFC and one for a Spur and of course check end-to-end readings anyway. I got lucky first time and first two brown wires were showing continuity. As did the blue's and the CPC. I then moved a clip to the 3rd cable to double check and my Metrel tester made the dull sound when it refuses to test, showing 29v L-CPC.

As this was in a cellar, I was a bit naughty and had the board and lighting circuit live while testing other circuits.
When I traced the cable concerned I found it ran very parallel to the live lighting circuit for a long distance, and ended up at a socket with a very long extension lead plugged in. Unplugging the extension lead was enough to make the tester happy and prove what I'd worked out anyway by then, the cable wasn't connected to anything else.
 

Reply to Induced voltage on twin and earth cable in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi everyone, When checking my consumer unit voltages with the full board off, I stumbled across something head scratching. Measuring the feed...
Replies
1
Views
575
I see they're introducing a new type of flat twin cable with a sheathed CPC. In my location there's no requirement to sleeve CPC/bonding...
Replies
21
Views
2K
hi....im running cable for a split type 1.5 hp aircon....i have a roll of english 2.5 twin & earth, is this ok for the job? im running it to the...
Replies
0
Views
228
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
501

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock