It may be completely stupid but I've been wondering about this one for a while...

Short of coming back at night, how do I get Ze or do the RCD testing for an economy 7 system?
 
Last one I did had no seals on the clock so I just advanced it. Otherwise a set of leads from the main CU, this will change the results slightly but should be for the worse so if they are OK you should also be OK on the proper tails.
 
I recently fitted a CU for Econ 7 which was not yet connected.

I took a live feed from the main CU with 10mm just to do the tests then connected the 25 mm tails for the DNO to connect when they changed the meter!

Dead tests would be OK for your certificate calculating the ZS. (But then your RCD needs testing)

ZE would be taken as you would normally do it at the premises!
 
Stay over night with the customer ;)

I think you mean Zs? As said I'd run some temporary tails to test and note the certificate accordingly. If minor job calculate Zs
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined

Thread Information

Title
Live tests on Economy 7?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
4

Advert

Thread statistics

Created
DNS1,
Last reply from
Shaun1987,
Replies
4
Views
1,954

Advert