Here's an interesting one... :)

Amongst other things, was asked to replace a 1G exterior socket with a 2G. Did some basic checks before I started, including IR (L+N to E) on the RCBO-protected socket RFC. ~0.26MΩ, uh oh. Sigh theatrically, ponders a day of unplugging everything then splitting down the ring etc.

However, given that the exterior socket was supplying a small pond fountain, I thought I'd try that first. Unplug it, and low and behold the IR reading goes up to a more healthy 27.4MΩ.

What initially struck me as odd was that the existing 1G socket was wired like this:

DSC_1466 copy.JPG

:eek:

So I tried a little experiment:

DSC_1468 copy.JPG


(test was done at 250V, tester says 0V as test had completed).

Logically, it all checks out... but it still amused me that I could just lightly poke my test probe into the gravel and it give pretty much the same reading I was getting in the house. :)
 
  • Like
Reactions: Jim_e_Jib and Wilko
What initially struck me as odd was that the existing 1G socket was wired like this

Mmmm..bet they disconnected that cpc to increase the earth fault impedance and reduce the leakage on that failing pump to get a bit more life out the old girl haha. That RCBO wouldn't stay in at 0.26 with cpc connected. Devils ain't they lol
 
  • Disagree
Reactions: westward10
Mmmm..bet they disconnected that cpc to increase the earth fault impedance and reduce the leakage on that failing pump to get a bit more life out the old girl haha. That RCBO wouldn't stay in at 0.26 with cpc connected. Devils ain't they lol

The RCBO shouldn't trip with an L-E IR of 0.26M ohm... that's a leakage current of 0.9mA.
 
The RCBO shouldn't trip with an L-E IR of 0.26M ohm... that's a leakage current of 0.9mA.

Yep, indeed, I stand corrected. About 0.10M ohm is more like it going that the 30ma's trip on ramp at around 22ma I find.

Still a ropey old pump though and well ready for the bin!
 
  • Agree
Reactions: SparkyChick
Against my advice, the client has continued to use the old fountain pump, and no it doesn't trip the RCBO. They promised they'll look into getting a new one.

I see what you mean about the aesthetics of the KT63, it is a bit random! :) But I do like my little Kewtech - you can tell what every button does, you don't have to remember things like, "F3 for null" or "<--> for a different setting."
 
Yep, indeed, I stand corrected. About 0.10M ohm is more like it going that the 30ma's trip on ramp at around 22ma I find.

Still a ropey old pump though and well ready for the bin!
Wouldn't that be a trip at around 0.01MΩ at 22mA, not 0.1MΩ?
 
Against my advice, the client has continued to use the old fountain pump, and no it doesn't trip the RCBO. They promised they'll look into getting a new one.

I see what you mean about the aesthetics of the KT63, it is a bit random! :) But I do like my little Kewtech - you can tell what every button does, you don't have to remember things like, "F3 for null" or "<--> for a different setting."
Hi Steve.

I've sometimes got poor IR results and then when everything is unplugged they disappear. In otherwords it's the appliance that is 'possibly' faulty.

I remember DaveSparks reminding me once that when we IR test we are just testing the fixed wiring. I personally don't have enough knowledge of each appliance to know whether it should have any kind of pathway to earth and if a measurement of <1MΩ signifies a faulty appliance. Would a PAT test not be required in this case before recommending an appliance not be used. (Saying that, I do remember back when I started I traced poor IR results to an extension lead and suggested it was faulty, all it was was surge protection! :rolleyes:). I also remember lucien explaining that it is rare for an appliance to have an intended 'lower' IR reading to earth but not impossible.

I''d be putting the CPC back into the socket rather than the box and putting the reading as 27.4MΩ as that is the correct reading for the fixed wiring. I would still advise the customer to get the pump looked at but I'd make it clear that I can't say for sure if it is faulty.

Of course, saying all that, you have a better understanding of these things than I do, plus you've worked with boats where I guess you dealt with pumps.... so perhaps you can say it's faulty. I shall await to be put in my place :)
 
  • Agree
Reactions: happysteve
I replaced the cover on my brothers outdoor socket. CPC terminated into the back box as well. Wonder if it was the same sparks :)
 
  • Funny
Reactions: happysteve
I replaced the cover on my brothers outdoor socket. CPC terminated into the back box as well. Wonder if it was the same sparks :)
That weren't no spark. From the client's recollection, it was "the blokes that put up the conservatory." Kinda figures...

Why provide the earth terminal at all? I can see the point on a surface mount pattress (if used for single pole switches) but putting one on a socket enclosure, I just feel like the manufacturers are trolling us. "We'll just put this here, see if anyone falls for the bait..." :)
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

happysteve

Broke Internet
Arms
~
Joined
Location
Nottingham
Website
http://www.dovecote-electrical.co.uk
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)
Business Name
Dovecote Electrical

Thread Information

Title
Low IR to earth (with no CPC)
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
14

Advert

Thread statistics

Created
happysteve,
Last reply from
happysteve,
Replies
14
Views
1,897

Advert