Here's an interesting one... 
Amongst other things, was asked to replace a 1G exterior socket with a 2G. Did some basic checks before I started, including IR (L+N to E) on the RCBO-protected socket RFC. ~0.26MΩ, uh oh. Sigh theatrically, ponders a day of unplugging everything then splitting down the ring etc.
However, given that the exterior socket was supplying a small pond fountain, I thought I'd try that first. Unplug it, and low and behold the IR reading goes up to a more healthy 27.4MΩ.
What initially struck me as odd was that the existing 1G socket was wired like this:

So I tried a little experiment:
(test was done at 250V, tester says 0V as test had completed).
Logically, it all checks out... but it still amused me that I could just lightly poke my test probe into the gravel and it give pretty much the same reading I was getting in the house.

Amongst other things, was asked to replace a 1G exterior socket with a 2G. Did some basic checks before I started, including IR (L+N to E) on the RCBO-protected socket RFC. ~0.26MΩ, uh oh. Sigh theatrically, ponders a day of unplugging everything then splitting down the ring etc.
However, given that the exterior socket was supplying a small pond fountain, I thought I'd try that first. Unplug it, and low and behold the IR reading goes up to a more healthy 27.4MΩ.
What initially struck me as odd was that the existing 1G socket was wired like this:

So I tried a little experiment:
(test was done at 250V, tester says 0V as test had completed).
Logically, it all checks out... but it still amused me that I could just lightly poke my test probe into the gravel and it give pretty much the same reading I was getting in the house.