Fitted a new light fitting for my daughter in her living room it was a BnQ jobby but the terminals were suprisinly good and plenty of room too . She only had 2 bulbs 40w candle ses so fitted these all seemed ok.
Got called back the day after to see 5 new leds fitted but buzzing like mad. as the lamps looked like the crap from poundland I removed them and tested them in another fitting all was good and quiet too.Rechecked everything all seemed fine but the 6A circuit breaker was buzzing too and another led lamp in a separate fitting in the kitchen was flashing???? all was ok when the living room light was turned off .
So checked the switch immediatly noticed it was 2 way asked where is other switch? behind curtains she replied and yes it was a dimmer swapped it and the problem has gone. Seems the drivers when under voltage can do funny things.
 
Is that common then or what?
 
Dimmer, Driver, and Led must be compatible or all sorts of things an happen.
Also standard dimmers only start working if load is >40VA. Most LEDs are less than that.
So you may need to look at a low-watt led compatible dimmer. V-PRO are good.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
New Light Fitting Buzzing
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
3

Advert

Thread statistics

Created
Barry White,
Last reply from
Barry White,
Replies
3
Views
4,564

Advert