Murdoch, the only one of those that you don't have free access to is GN5.And how many of us have , or have ready access to all of these ?
Murdoch, the only one of those that you don't have free access to is GN5.And how many of us have , or have ready access to all of these ?
Murdoch, the only one of those that you don't have free access to is GN5.
Are you going to ignore ‘manufacturers instructions’? And are you going to let us all know what ‘SWA glands’ are produced for if not to go on SWA cable?Are you EVER going to quote a BS 7671 reg that states clearly that SWA must be earthed at the supply end ?
Does it?ditto. Being a member of the IET and registered with the engineering council has its perks.
So where does it say in the regs you run can export the DNO earth?!It is a requirement of ESQCR (Reg 24 I believe) for the DNO to provide consumers a connection point to either the network neutral or protective conductor, for connection of the installation earth.
Regulation 25 allows the DNO to refuse this connection only if the installation fails to comply with BS7671, or could pose a danger or cause an interruption of supply.
So where does it say in the regs you run can export the DNO earth?!It is a requirement of ESQCR (Reg 24 I believe) for the DNO to provide consumers a connection point to either the network neutral or protective conductor, for connection of the installation earth.
Regulation 25 allows the DNO to refuse this connection only if the installation fails to comply with BS7671, or could pose a danger or cause an interruption of supply.
What’s your membership number?Does it?
Can’t say I’ve really noticed.
Are you going to ignore ‘manufacturers instructions’? And are you going to let us all know what ‘SWA glands’ are produced for if not to go on SWA cable?
SWA is an extraneous conductive part......go back to college.
134.1.1
That is the answer......134.1.1 and you don’t understand because you have’nt got enough experience or training. There’s only 2 places I can name where you insulate SWA from connection.That DOES NOT answer my question, the question that has haunted this thread for pages
Please answer my question ......
That ‘given earth’ is for ‘that equipotential zone’Sorry mate, but you have now gone beyond my simple mind. I've read the references you've kindly provided and I can't see a problem using an already in place TNCS/PME DNO cutout to supply the shed. No going to jail that I can see, provided it's done in accord with our usual BS7671. What have I missed ?
More importantly, where does it say you cannot?So where does it say in the regs you run can export the DNO earth?!
That ‘given earth’ is for ‘that equipotential zone’
You won’t understand because you can’t grasp the importance of an equipotential zone on a tncs supply. So I 100% know you will never understand. So will stop there with you.
Because it is in the HOUSE and running through the fabric of the HOUSE and in the HOUSE equipotential zone...because it’s an extraneous conductive part.....and not with a strap but with an SWA gland 134.1.1The question was and still is WHERE DOES IT STATE THAT THE ARMOUR MUST BE CONNECTED TO EARTH AT THE SUPPLY END
Nothing more to say to you.Arrogant and extremely disrespectful !
Look at that you are slowly working out how a ‘guide book’ works....More importantly, where does it say you cannot?
Membership No. 86042686.
Now you’re being a dick.Look at that you are slowly working out how a ‘guide book’ works....
Because it is in the HOUSE and running through the fabric of the HOUSE and in the HOUSE equipotential zone...because it’s an extraneous conductive part.....and not with a strap but with an SWA gland 134.1.1
1100194966So where does it say in the regs you run can export the DNO earth?!
What’s your membership number?
It appears you are 2 digits short of an IET membership number. On your card what is your area number?Lol, don’t want to make a big thing about it, but it appears I’ve been a member for a lot longer than you.
An extraneous conductive part in a house doesn’t need bonding to earth.......kind of invalidated most of your last and final comment.Look you clearly don't seem to realise [or care] that there are many well qualified,highly experienced and dedicated professional electricians on this forum. Nowhere has it been suggested using a strap instead of an SWA gland, although this was common practice for many years and I'd imagine considered acceptable at one time. Of course the armour must be connected to earth, you do realise that we're talking about situations where a seperate CPC is used within the cable ? But I still say that it doesn't state anywhere that the armouring MUST be earthed at the supply end. I've had enough of this nonsense now and won't post any more on this thread.
Oh you call it extending? How very modern.Anyway where is this place we are exporting things to? Will we be able to export them when we leave the EU? Arghhhhhh..........
Or did you mean extending??