Not sure that the difference between a MET and an EMT has any significance?
Regulation 8 of the EAWR is not particularly complicated, though it is a bit contradictory.
Tells us to earth all conductors not intended to be live, which obviously contradicts Regulation 9.
 
  • Like
Reactions: Dave OCD
Is BigBob1 NetblindPaul in disguise ? They're equally good at generating irrelevant posts, never being wrong and avoiding the answers to very simple questions by spouting an abundance of waffle.
 
As it happens I have access to all of the listed publications, though my copy of GN5 is probably out of date.
 
yes consult the DNO. It is their Earth not yours. It’s their TX not yours. It is their engineers that calculate where and when a neutral can be used as CNE.

No if you ask them for permission and they say ‘yes’ then you can. Obviously.


With TT systems, the consumer must provide his or her own connection to Earth, i.e. by installing a suitable earth electrode local to the installation. The circumstances in which a distributor will not provide a means of earthing for the consumer are usually where the distributor cannot guarantee the earth connection back to the source, (IET)

IET. Guidance Note 5: Protection Against Electric Shock, 7th Edition.

That means you are guaranteeing it! But it’s not yours! ESQCR 24 you will be in jail.

installations supplied from TN-C-S (PME) systems, in view of the risk of danger in the event of an open circuit neutral fault on the distributor's low voltage network. ESQCR Regulation 25(2) prevents a distributor from providing a PME supply to premises (IET)
IET. Guidance Note 5: Protection Against Electric Shock, 7th Edition.

ESQCR 25 (2). Taking a DNO supply and provided earthing arrangement out of their specified equipotential zone. Jail.

You do understand that out of all the documents electricians ‘use’ BS7671 is the last one! And it starts with EAWR 89 and ends with ESQCR....with HASAWA and CDM regulations in between...
 
I’ll let you in on a little known secret....

While the publisher and contributors believe that the information and guidance given in this work is correct, all parties must rely upon their own skill and judgement when making use of it. The publisher and contributors do not assume any liability to anyone for any loss or damage caused by any error or omission in the work, whether such error or omission is the result of negligence or any other cause. Any and all such liability is disclaimed. (IET)

IET. BS 7671:2018 Requirements for Electrical Installations, IET Wiring Regulations, 18th Edition.
 
Are you EVER going to quote a BS 7671 reg that states clearly that SWA must be earthed at the supply end ?
Are you going to ignore ‘manufacturers instructions’? And are you going to let us all know what ‘SWA glands’ are produced for if not to go on SWA cable?
SWA is an extraneous conductive part......go back to college.
134.1.1
 
It is a requirement of ESQCR (Reg 24 I believe) for the DNO to provide consumers a connection point to either the network neutral or protective conductor, for connection of the installation earth.
Regulation 25 allows the DNO to refuse this connection only if the installation fails to comply with BS7671, or could pose a danger or cause an interruption of supply.
 
‘I don’t have to do a risk assessment because it doesn’t say so in the regs’ Said the domestic installer.

114.1
 
I rest my case.
 
  • Agree
Reactions: Pete999
It is a requirement of ESQCR (Reg 24 I believe) for the DNO to provide consumers a connection point to either the network neutral or protective conductor, for connection of the installation earth.
Regulation 25 allows the DNO to refuse this connection only if the installation fails to comply with BS7671, or could pose a danger or cause an interruption of supply.
So where does it say in the regs you run can export the DNO earth?!
 
It is a requirement of ESQCR (Reg 24 I believe) for the DNO to provide consumers a connection point to either the network neutral or protective conductor, for connection of the installation earth.
Regulation 25 allows the DNO to refuse this connection only if the installation fails to comply with BS7671, or could pose a danger or cause an interruption of supply.
So where does it say in the regs you run can export the DNO earth?!
Does it?
Can’t say I’ve really noticed.
What’s your membership number?
 
My take on this is that any paid work being done, no matter the location, comes under HASAWA and EAWR, this includes domestic properties.
Because the requirements are to maintain safety, this must be done during the works and can be achieved, electrically, by following BS7671.
Therefore, only if there are no changes, after the work has finished it must not present a danger; if it does present a danger then the work that was being done was not, at that time, in accordance with the law.
In that respect the HASAWA and EAWR do apply to the work once it is completed (but most defences would claim later changes had been made!). However when no one is actually working in a domestic property the HASAWA and EAWR do not apply to what is happening in the present, only to the effects that had happened in the past.

Regarding SWA I do not believe it is required to earth the armour, that is not being used as a cpc, at the supply end; it is just best practice. The shorter fault path leads to better compliance with the minimum standards of BS7671 by reducing the impedance of the fault path.
Earthing the armour at both ends, when it is not a cpc, may lead to circulating currents through the armour, but the level of disadvantage must be weighed up against the advantages of having two earthed points on an exposed conductive part.
However where the two ends are in installations with different earthing arrangements then 542.1.3 applies and the supply end only must be earthed.
The default case of the armour as a cpc clearly requires continuity and therefore earthing at both ends.
 
Are you going to ignore ‘manufacturers instructions’? And are you going to let us all know what ‘SWA glands’ are produced for if not to go on SWA cable?
SWA is an extraneous conductive part......go back to college.
134.1.1

That DOES NOT answer my question, the question that has haunted this thread for pages

Please answer my question ......
 
  • Like
Reactions: Dave OCD
Sorry @bigbob1 but you have gone beyond my simple mind. I've read the references you've kindly provided and I can't see a problem using an already in place TNCS/PME DNO cutout to supply a shed. No going to jail that I can see, provided it's done in accord with our usual BS7671. What have I missed ?
 
Last edited by a moderator:
That DOES NOT answer my question, the question that has haunted this thread for pages

Please answer my question ......
That is the answer......134.1.1 and you don’t understand because you have’nt got enough experience or training. There’s only 2 places I can name where you insulate SWA from connection.

Using VSD’s
And leaving equipotential zones.
 
The question was and still is WHERE DOES IT STATE THAT THE ARMOUR MUST BE CONNECTED TO EARTH AT THE SUPPLY END
 
Sorry mate, but you have now gone beyond my simple mind. I've read the references you've kindly provided and I can't see a problem using an already in place TNCS/PME DNO cutout to supply the shed. No going to jail that I can see, provided it's done in accord with our usual BS7671. What have I missed ?
That ‘given earth’ is for ‘that equipotential zone’

You won’t understand because you can’t grasp the importance of an equipotential zone on a tncs supply. So I 100% know you will never understand. So will stop there with you.
 
  • Dislike
Reactions: DPG and Wes1000
That ‘given earth’ is for ‘that equipotential zone’

You won’t understand because you can’t grasp the importance of an equipotential zone on a tncs supply. So I 100% know you will never understand. So will stop there with you.

Arrogant and extremely disrespectful !
 
The question was and still is WHERE DOES IT STATE THAT THE ARMOUR MUST BE CONNECTED TO EARTH AT THE SUPPLY END
Because it is in the HOUSE and running through the fabric of the HOUSE and in the HOUSE equipotential zone...because it’s an extraneous conductive part.....and not with a strap but with an SWA gland 134.1.1
 
The thing about Bigbob1 and his arguments, is that they are not based in fact and he cannot back up anything he states.
If a law of physics prevents us from doing something, permission from the DNO will not suddenly allow us to do it.
GN5 (although my copy is from 2004) makes no mention of us not being allowed to export any earthing system.
Same applies to ESQCR and EAWR.
In fact, ESQCR requires the DNO to allow me to export the earthing system, the only reasons they can refuse is if the installation does not comply with BS7671, is unsafe or if it might cause a disruption in network supply.
 
Because it is in the HOUSE and running through the fabric of the HOUSE and in the HOUSE equipotential zone...because it’s an extraneous conductive part.....and not with a strap but with an SWA gland 134.1.1

Look you clearly don't seem to realise [or care] that there are many well qualified,highly experienced and dedicated professional electricians on this forum. Nowhere has it been suggested using a strap instead of an SWA gland, although this was common practice for many years and I'd imagine considered acceptable at one time. Of course the armour must be connected to earth, you do realise that we're talking about situations where a seperate CPC is used within the cable ? But I still say that it doesn't state anywhere that the armouring MUST be earthed at the supply end. I've had enough of this nonsense now and won't post any more on this thread.
 
  • Like
Reactions: DPG and 123
I think big bad bob has been educated beyond his intelligence, as a mate of mine used to say. he obviously does not operate in the real world, out there. The world of sheds, and things.
 
Anyway where is this place we are exporting things to? Will we be able to export them when we leave the EU? Arghhhhhh..........
Or did you mean extending??
 
  • Like
Reactions: DPG
Look you clearly don't seem to realise [or care] that there are many well qualified,highly experienced and dedicated professional electricians on this forum. Nowhere has it been suggested using a strap instead of an SWA gland, although this was common practice for many years and I'd imagine considered acceptable at one time. Of course the armour must be connected to earth, you do realise that we're talking about situations where a seperate CPC is used within the cable ? But I still say that it doesn't state anywhere that the armouring MUST be earthed at the supply end. I've had enough of this nonsense now and won't post any more on this thread.
An extraneous conductive part in a house doesn’t need bonding to earth.......kind of invalidated most of your last and final comment.
 
I'll have to reply again, what I'm saying is it CAN be connected to earth at the far end - as long as it's connected. You're clearly less intelligent than you think you are.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
New sub board for shed swa advice.
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
308

Advert

Thread statistics

Created
Jcamerz,
Last reply from
Pete999,
Replies
308
Views
27,810

Advert