That’s pretty much what I said apart from the N/A if it’s 5 circuits on same rcd I repeat the 5 readings on 5 mcbs. If there are 5 rcbos then the 5 readings will be recorded independentlyI write the rccb in the circuit column if it’s a split load board, 61008, it’s current rating etc then I record only one rcd trip time measurement,I do not repeat the measurement to correspond to each circuit, for the column that covers 60898 devices I put N/A as it’s an mcb and not an rcbo.
Totally agree with you here. I was thinking how to record this and came up with the same idea.Because I write the circuits underneath, then if there’s another rcd the other circuits are written under that one,
Just how I do it, by no means am I suggesting that it’s the be all and end all of doing it, as long as the information is recorded.