Discuss OK to T consumer unit for garage off existing SWA to workshop? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
I currently have a 10mm T&E SWA cable (which passes through my garage) serving a small CU in my workshop at the bottom of my garden (200ft). The garage is currently connected to a FCU on the downstairs ring, but I would like to T off the SWA and add another consumer unit in the garage.
First and foremost I would like to confirm this is an acceptable thing to do in principle.
No doubt some of you will be interested in additional parameters, so to flesh things out a bit:
The SWA is connected to a 40A MCB and 30 mA RCD in a small CU that has been fitted in the meter box (independent of the main house CU). (I appreciate I will need to consider the overall load/diversity for the property.)
The workshop has a 6A lighting circuit and a 20A Radial. I am proposing to fit the same in the garage.
Oh I should mention that when the CU was fitted in the workshop an Earth Rod was added outside.
Any guidance/thoughts appreciated as long as someone answers the primary question first.
In principle there is nothing wrong with a submain which feeds two points.
Your post isn’t too clear as to whether it is SWA or T&E as you mention both?
I take it that you understand from the description of the intallation, that consumption of Electricity is restricted to 13 Amps, as you have taken the feed to the Shed from a fused spur from the downstairs RFC.
I think the existing garage feed is off the FCU, the existing garden shed feed that is to be intercepted is three core SWA on a 40A MCB with a 30mA RCD.
Ah yes Rich you are right I missed that, sorry OP, message Pete999 read the bluudy post properly.
Reply to OK to T consumer unit for garage off existing SWA to workshop? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Hi all, My mother wants a double socket adding next to a desk, behind the desk there is a 10mm (i dont know the MCB in the Consumer Unit) which...
Currently I have a Henley block which has 2 consumer units. 1 of these CU feeds a garden supply and garage. Out in the garden which is fed by a...
Hi Guys, hopefully someone will know the answer. Testing an install on a (domestic) PME system I have a garage consumer unit supplied from one of...
Trying to organise a CU replacement at home. It's a 1930s property. It's got a 10way CU but with no RCD protection. Was after a larger unit with...
4K