Hi all

The subject says it all - there's a lot of outside exposed clipped t&e out there with all the attendant physical protection and UV issues.

Question is - should it have a fault code on a report? I guess it would be a C3 at most, but should it feature at all?

Cheers
 
C3 or just a comment in my book
 
no code ,but how ever you could put C3 . you the test master must think about it .
 
See Regulation 522.11
 
If it’s a short stretch of cable from say a hole to a light then no code

if its yards of cable clipped all around the house getting baked in the sun but no visible damage then code3

if It’s visibly badly damaged And crumbly to the touch then code2
 
The length of cable is irrelevant.
 
522.11.1 - suitable for UV conditions.
IMHO PVC t&e isn't, so I'm going C3 especially as some of it is unclipped so attention is needed anyway

It being unclipped is a seperate issue to be reported seperately.

If the cable shows signs of UV damage, or severe UV damage then code accordingly,
 
  • Agree
Reactions: Baddegg
Depends, on a few factors...
Use your engineering judgement and be confident in your decision.
Books are good for guidance but they cant account for every situation.
You could code this C1 C2 or C3. Maybe no code.

I'd check If it's all gone brittle or not, and where it is? I'd personally code it differently depending on risk.
If it's at a school where kids might pick snd pull at it you may want to code it as a C2.
A small section going into a 500w flood light high level in someone's back garden in good condition is probably most likely ust a C3
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Doncaster
Business Name
Beacon Electrical

Thread Information

Title
Outdoor t&e - EICR fault code?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
10

Advert

Thread statistics

Created
Richard Measures,
Last reply from
AJshep,
Replies
10
Views
8,882

Advert