Hi all
The subject says it all - there's a lot of outside exposed clipped t&e out there with all the attendant physical protection and UV issues.
Question is - should it have a fault code on a report? I guess it would be a C3 at most, but should it feature at all?
Cheers
If it’s a short stretch of cable from say a hole to a light then no code
if its yards of cable clipped all around the house getting baked in the sun but no visible damage then code3
if It’s visibly badly damaged And crumbly to the touch then code2
Depends, on a few factors...
Use your engineering judgement and be confident in your decision.
Books are good for guidance but they cant account for every situation.
You could code this C1 C2 or C3. Maybe no code.
I'd check If it's all gone brittle or not, and where it is? I'd personally code it differently depending on risk.
If it's at a school where kids might pick snd pull at it you may want to code it as a C2.
A small section going into a 500w flood light high level in someone's back garden in good condition is probably most likely ust a C3
Reply to Outdoor t&e - EICR fault code? in the UK Electrical Forum area at ElectriciansForums.net
Another thread asked about two circuits sharing a common multi-core cable and regulation 521.8.1 was mentioned. A friend of mine has inherited...
Good Afternoon All Currently doing an EICR on common parts of a big site with multiple blocks. All blocks have outside garden spike lighting in...
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Can someone sanity check my thinking please.... An 80 amp PME service head, tails to meter, 25 sq mm tails into an enclosed fused isolator with...