pjgtech

Hi, I am a basic DIY'er, with basic electrical skills, NB, I can change a plug/fuse, change a ceiling light fitting, change a socket face plate, install a ceiling fan, immersion heater, extractor fan, etc.

I already have one external outdoor weatherproof IP66 double socket at one end of my patio (connected to a socket in kitchen), already fitted when I moved in last year and it works fine.
I would like an additional outdoor weatherproof socket at the other end of my garden (it would be connected to a socket in the newly installed log cabin, which has its own separate consumer unit, etc).

I have been looking at the various outdoor IP66 ones, some have RCD protection built in and some don't.
To wire in a non RCD unit I understand its a simple matter of connecting a cable from the unit (Earth Neutral and Live) through the wall to an 3 pin plug and then plugging into a socket to power the unit. NB: some of the units come with the cable and plug.
However, if the outdoor weatherproof unit has built in RCD protection does it need to be wired differently or the same as a unit with no RCD protection built in?
I assume that the ones with RCD protection built in are better as theres an extra layer of protection?

For extra info the house is only four years old, so has a new and well protected electrical system, eg: split consumer unit with protection , etc..

The new external weatherproof IP66 socket will be used for outside lights (low voltage LEDs) and a hot tub.
I have an electric mower so that does not need electric, and I use the already existing outdoor socket for my electric hedge trimmer, strimmer and leaf mulcher.

Any info / advice gratefully received....
Cheers
 
If the house wiring is only 4 years old and the sockets already have RCD protection, then it would be pointless to install a socket with built in RCD. Two 30mA RCDs in series not recommended.
 
biggest concern is the loading of the hot tub. some come with plug and 10mA RCD built in. these can be plugged in directly to the socket. you're looking at about 10A for this type.
 
Yep, will just be a plug in cheapo type hot tub, LazySpa Hawaii model I think it has built in RCDprotection 10ma device.
 
As far as the outside socket goes, I’d get someone in to do it properly… connected to the consumer unit in the cabin…. Which will be done professionally, I presume?

If it was just for a lawnmower, then these ready made extension leads are fine… but for a hot tub, I wouldn’t like to take the risk.
 
If you do put in a new socket then please test it before use. Ideally for DIY with something like this:


You can get cheaper socket testers and they are better than nothing, but the above sort of model has a more meaningful test of the earth fault loop impedance (some cheap ones would pass wet string as an earth connection) and has a button to simulate a fault to verify the RCD really trips as intended for protection.
 
  • Like
Reactions: PeakSteve
If you do put in a new socket then please test it before use. Ideally for DIY with something like this:


You can get cheaper socket testers and they are better than nothing, but the above sort of model has a more meaningful test of the earth fault loop impedance (some cheap ones would pass wet string as an earth connection) and has a button to simulate a fault to verify the RCD really trips as intended for protection.
pricceyone that. mine just as good with also having LCD voltage.hertz. N-E volts. reading and a frction of the cost.

 
  • Like
Reactions: loz2754

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Email
Joined
Time zone
Last seen

Thread Information

Title
Outdoor weatherproof socket IP66 with RCD
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
7

Advert

Thread statistics

Created
pjgtech,
Last reply from
telectrix,
Replies
7
Views
2,664

Advert