Prosecution

Discuss Prosecution in the UK Electrical Forum area at ElectriciansForums.net

tigerpaul

-
Arms
Reaction score
101
We had our ECA assessor visit today and while we were chatting he mentioned a case in London where a contractor had done an apartment block. There was a fan in a bathroom which had gotten stuck and the motor had caught alight and caused a major fire. Everything he'd done was as per BS7671, except however he hadn't fused the fan down to 3A as per the fan manufacturers instructions. Now this contractor has been prosecuted.
Now how many times have you seem a bathroom fan fused down to 3A? I haven't at all, it's always just the 6A Mcb providing protection.
 
I think that if the manufacturer requires their equipment to be fused then they should install the relevant fuse in their equipment, then if the fuse blows it will require an electrician to change the fuse which should ensure that the reason for fuse failure is identified and rectified and that the a correctly rated replacement fuse is installed.
 
All the fans I've installed I've fused to 3A, as per manufacturer's instructions. I normally have those dual 1G boxes to hand for the purpose. The whole bathroom goes onto the FCU, with the fan iso along side.
 
This is what you need...
IMG_3119.jpgIMG_3118.jpg
 
Didn't somebody on here mention once they had some Chinese equipment they had to install and had manufactures instructions stating that neutrals were to be fused?

Would you still follow their instructions or the standard nic reply or would you apply professionalism to the incident? Just to throw a spanner in the works....
 
The switch and fuse holder are the Click Mode range. You buy modules an fit them into the normal face plates. 4 gang face plate would be a 2 gang back box. Or you could fit the fan isolator and bathroom light switch into a 3gang plate and 2 fuse holders into a 2gang plate next to it in a dual back box.
 
I dunno what your all going on about. There is no prosecution going on, it's just another tall story!! If anyone would get the blame (if it were true), it should be the fan manufacture. A 10/20W fan isn't going to be too well protected by a 3A HRC fuse or 6A MCB, so it's all academic, your all scaring yourself's silly, about something your not ultimately responsible for...
 
Didn't somebody on here mention once they had some Chinese equipment they had to install and had manufactures instructions stating that neutrals were to be fused?

Would you still follow their instructions or the standard nic reply or would you apply professionalism to the incident? Just to throw a spanner in the works....

i'd never follow manufacturers instructions that directly contradicted bs7671.
ie use your loaf ;-)
 

Reply to Prosecution in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top