I thought that but I'm not so sure. We need a picture from a lower angle to be sure.the rcd neutral connection on the bottom right goes to the bottom of the main switch instead of the rcd so the neutral is not connected through the neutral side of the rcd!
Sy
That consumer unit is awful, as soon as you take the cover off and see the mess like that alarm bells start ringing. I understand when cables are short and need to be crimped doesn’t help the matter but that is shocking no effort whatsoever on thereAnd I agree those tails have way to much copper showing!
Wait there I’ve just looked back they are all new colours and has plenty of cable length to terminate just makes it even worse. Wow that is dog rough.That consumer unit is awful, as soon as you take the cover off and see the mess like that alarm bells start ringing. I understand when cables are short and need to be crimped doesn’t help the matter but that is shocking no effort whatsoever on there
No cover on the busbar? Doubt it arrived like that. A lot of copper showing. Generally poor workmanship, my guess is no testing and wouldn't know how to find the fault anyway. What is the black tape in top corner also?sure thing, outside and inside.
On an unrelated note, are there any regs concerning how far back the insulation is stripped on the incoming tails? I don't like the fact there is a few mm of live tail showing and would have thought the tail insulation should touch the main switch body? I was told by a mate years ago when wiring sockets etc to never leave bare cable showing outside the terminals. This is how it was when fitted with the exception of the disconnected neutrals in the top right and also a groove I cut in the wall to the left in order to get the cover back on without stressing the breakers. I took care to cover the electrics with some plastic sheeting and masking take to avoid any debris getting inside.
yes, there is a neutral link from bottom of RCD to neutral, you just can't see it in that picture due to the camera angleIt looks from your photo that the neutral link to the terminals is in the bottom of the main switch, and there is no neutral link in the bottom of the rcd.
<snip image>
Black tape is to cover the exposed ends of the disconnected neutrals to stop them inadvertantly touching something they should not.No cover on the busbar? Doubt it arrived like that. A lot of copper showing. Generally poor workmanship, my guess is no testing and wouldn't know how to find the fault anyway. What is the black tape in top corner also?
Yes, only at night, no night storage heaters, no timed or light sensitive or PIR lights. Only things on overnight are the alarm, gas boiler and Google nest thermostat for said boiler.Thanks for clarifying the neutral link query.... im sure someone later will ask you again, as they wont read every post... #33... i'll remember.
A question though. Does it only trip during the night? That sounds like its a timed piece of equipment such as storage heating or off peak water heater. Maybe the neutrals are mixed up between the on and off peak immersions?
Scratch that.
Just looked at the original photos, and theres no off peak heating marked up.
Too late!I have deleted your video from your latest post as it shows the name of the contractor. If you can edit this out feel free to post it again.
Or a loose connection.Too late!
If the RCD turns itself off with no neutrals connected, and all MCBs fed from it also off, it can only be a dud RCD.