Blastfrom the Past . still out there . Yeah

Measurementof ( Ze ) Three-phase .

Older-method: ( Fuses )Still out there .
Fuse(s)must be .( removed ) to disconnect theInstallation for this test .
Live-test . Red .Yellow . Blue . ( Old-colourswill be still in Use )

Three-probes
1). Probes on disconnected - Earthing-conductor
2). Probes on Neutral .
3). Probe on Line . Red . Yellow . Blue .
Red- 0.25Ω .
Yellow- 0.26Ω .
Blue- 0.25Ω .
 
Useful junk

Determine of 3phase - fault-current .

Highest . single-phase value measured . = 2.28kA .( 2.28 x √ 3 = 3.95kA )
An . approximation can be done as ( 2 x ) the reading . i.e. ( 2 x 2.28 =4.56kA )

Minimum breaking capacity for protectivedevices kA

 
( R[SUP]1[/SUP] + R[SUP]2[/SUP] ) are the effective-résistances . to thefurthest-point
( 1.67 - relates to the ratio of résistance of . ( 2.5mm[SUP]2[/SUP] / 1.5mm[SUP]2 [/SUP] ) it won’twork for ( Other-sizes ) Ring-final-circuit Only .

( Zs ) Confirms that a (Satisfactorily-low-fault-path-exists ) to activate the . relevantprotective-devices .
 
UsefulJunk .

Nuisance-Tripping.
Certain-appliancessuch as Freezers tend to have . bynature of there construction & use . some leakage-currents to earth .

 
433.1.103. - Ring-final-circuit(s) p.81.
MinimumC.S.A. of PVC-cables . 2.5mm[SUP]2[/SUP]
MinimumC.S.A. of ( MI ) cables . 1.5mm[SUP]2[/SUP]
Minimum-current-carrying-capacityof . Line & Neutral-conductor(s) - ( Iz) 20A - device . 433.1.1
Theload-current should not-exceed what for . long-periods . Current-carrying-capacity of the cable ( Iz ) of the cable .
British-standardsof . accessories to be . BS-1363 .
Overcurrent-device to be rated at . 30A or 32A . protective-device .
 
Residual-current - Making me . ( dual-current )

TheRCD is designed to trip out when the difference between the . Line-current andthe Neutral-current ( So this is called the . residual-current) reaches the tripping-value . ( or rating ) of the device .
- Sensitivity: IΔn

RCD- Sensitivity is expressed as the rated-residual-operating-current ( IΔn ) .

TheTerm . RCD . is a generic-term applied . which open automatically in response toa . residual-current . equal to or greater than the RCDs - rated-residual-operating-current ( IΔn )
 
RCDsfall into two-categories in term of the time taken to respond . BS-EN -

(G ) General-type . These RCDs have no specified-minimum-response-time . but have specified . Maximum-response-times.
IΔn ≤ 300mS
5x IΔn ≤ 40mS .

(S ) Type : Known as . delayed-types . specified . Minimum and Maximum-response-times .
IΔn ≤ 130- 500mS
5x IΔn ≤ 150mS
 
RCDmaximum ( Zs- Ω ) or ( R[SUP]A[/SUP] - Ω )values .
IΔn- ( A ) maximum-touch-voltage - ( 50V )

30mA ) 0.03A - 1667Ω .
100mA ) . 0.1A - 500Ω .
300mA ) . 0.3A - 167Ω .
500mA ) . 0.5A - 100Ω .

- R[SUP]A [/SUP]≤ 50V ÷ 0.03A = 1667Ω . IΔn - 30mA
- R[SUP]A [/SUP]≤ 50V ÷ 0.3A = 167Ω . IΔn - 300mA
 
Test-procedure: your reason .
Theobject of continuity-testing . is to measure only the résistance of the partsof the wiring-system under test . T&E .

Whatis . Earth-fault-loop-impedance .

The path followed by . fault-current as a result of alow-impedance fault occurring between the . Line-conductor and Earth . & Earth-fault-loop . Fault-current is driven round the loop by thesupply-voltage . the amount of currentdepending on the voltage of the supply and on the impedance of the loop . The higher the impedance . the lower will be thefault-current . and the longer it will take for the circuit-protective-device operate and interrupt the fault . Loop-impedance must be low . to ensure that circuit-breakers will operatequickly enough in the event of a fault . The actual maximum-value depending on the . characteristics of the . circuit-breaker concerned . 2394: Testing of - Circuit(s) must be tested to make sure that the actual . loop-impedance does notexceed that specified for the protective-device ( Circuit-loop-impedance )
 
Whytwo -RCDs . split-load .2394 :
The circuits need to be divided evenly between two-RCDs to ensure some . lighting & power remainsif one operates .

RCD- ( G ) general-use . for Instantaneous
 
IEC-479-1 :

A residual-current-device . will ( Reduce ) the risk of Electric-shock .

Providedit has a residual-operating-current . not exceeding 30mA. & an operating-time not exceeding. 40mS . when a residual-current of 150mA - flows .
Thesecharacteristics are derived from the graph-shown . effects of current on thehuman-body can tolerate verysmall-currents for reasonably-long-periods . & moderate-currents forvery-short-periods .

Conductor(s): résistance .
Theease by which a . material-conducts electricity . is known as - résistance .

Conductor(s)- Interpreting .

Neutral-conductor. is defined as a . Live-conductor .
p.31: Neutral-conductor - A conductor connected to the . neutral-point of a system .& ( Contributing ) tothe transmission of ( Electrical-energy )

p.30: definition of - Live-conductor . refersto the . definition for . Live-parts .
Live-parts- a conductor or conductive-part intended to be . energized innormal-use . ( Including ) a neutral-conductor . Etc . This confirms that the . Line &Neutral-conductors . are both . Live-conductor(s) when energised .

(G ) RCD - device . as the earth-fault-current - ( If ) is . likely to be much higher than the . IΔn settings of the device installed . 30mA ÷ 1000 = 0.03A .
 
2394:
Circuit-breakers. ( is both a Circuit-breaking-device ) Emergency / switching . Table - 53.4.

Overcurrents- are detected by . three-different-devices .
-Thermal for Overloads .
-Magnetic releases . which aregenerally-combined - ( Thermal / Magnetic-circuit-breakers )

2394: Very basics . BS-EN-60898 - Manual or Automatic-control - of acircuit .

Circuit-breakersare identified with . Two-breaking-capacities .

6kA )- . BS-EN-60898- standard for household or similar-applications. where Unqualified-persons. can re-closes a circuit with a persistent fault-several-times . the breaking-capacity - in Amps .
p.285 . BS-EN-60898- 1 .Specification for circuit-breakers for . Overcurrent-protection . for household & similar-installations.

p.286. BS-EN-60947-2 . Circuit-breakers 10kA . Qualified-persons .

p.149. Circuit-breakers : Table-53.4.
BS-EN-60898 .
BS-EN-60947-2.
BS-EN-61009-1.

Donot get mix up .

BS-EN-60947 . Low-voltage . switchgear & control-gear .

BS-EN-60947-2. Circuit-breakers - 2006 .
 
Table- 41.2. : 41.4 : Type of fuses .
Fusesare indentified by . 2 - letters . according to their application-category . in ( LV-installation )

Thefirst-letter . indicates the . main-operation . ( g ) = general .
Thesecond-letter . indicates the . categoryof equipment to be protected .
G) protection of cables & conductors.
M) protection of . motor-circuits .
(gG ) - ( gM )

 
DNO: It is noted that .Supply-cut-out-fuses . are allowed to be utilized for overload-protection . ofthe main-supply-cables - 433.3.1.


Note : we are using thecircuit-breaker-side BS-EN-61009-1 .
Note : Regulations - 41.3. BS-EN-60898 & BS-EN-61009-1 .
Maximum-earth-fault-loop-impedance. ( Zs ) for circuit-breakers with . Uoof 230V . for . ( Instantaneous-operation ) Etc .

Domestic-installationsthe . ( PFC ) is unlikely to exceed . 6kA . up to which value the . [ Icn ] & [ Ics ] valuesare the same .
PlainEnglish - Note . Two-rated-short-circuit-ratings. protective-devices . BS-EN-60898 & BS-EN-61009-1 .

GN-3: p.100 - reminds us . Generic Scheduleof Test Results .
3). BS ( EN ) enter the . standard of manufacture of the .circuit-protective-device . e.g.
4). Type - where relevant for . circuit-breakers enter the sensitivity type .e.g. - C . ( B . C. D . time-characteristics )
5). Rating - enter the .protective-device-current-rating .
6). Breaking-capacity - enter the . protective-device-breaking-capacity . often “printed on the circuit-breakers “ e.g. 6.

GN-3- p.56 . [ Icn ] & [ Ics ] Two-rated-short-circuit-ratings. table - 2.8. [ Icn - 6 ] & [ Ics -6.0 ]
BS-EN-60898 & BS-EN-61009-1 .
[ Icn ] - is themaximum-fault-current . the device can interrupt safely . …….. [ Icn ] value is normally marked on the device [ 6000 ]
[ Ics ] - is the maximum-fault-current . the device caninterrupt safely without loss of . performance .

6). Breaking-capacity - enter the . protective-device-breaking-capacity . often “printed on the circuit-breakers “ e.g. 6.
For- domestic-installations . the ( PFC ) is unlikely to exceed 6kA . up to which value . [ Icn] will equal [ Ics ]

411.4.7.: where a circuit-breaker . Table- 41.3. for the types & ratings . ofovercurrent-devices . listed may be used . instead of calculation .
wherea circuit-breaker - BS-EN-60898 & BS-EN-61009-1 .
2394: our circuits . are . 411.3.2.2. Maximum-disconnection-times . Final-circuits . Notexceeding 32A . [ 0.4s ]




 
2394: Am making a Point to Note . can’tstress the importance of GN-3 . with Testing& Inspection . “ simplicity at isbest “

GN-3: Ambient-temperature 10°C . 20°C . ( 2394: regulations - 30°C . 70°C )

GN-3: Table - A4 .
Circuit-breakers. Maximum-measured-earth-fault-loop-impedance ( in Ohms ) at ambient-temperature 10°C . where the overcurrent-device is a circuit-breaker .BS-EN-60898 or RCBO to BE-EN-61009-1 .

Ambient-temperature 10°C
GN-3: in comparison .( C ) 6A - 3.09 . 10A - 1.85 .

(B ) 32A - 1.16
Table- A6 : ambient-temperature - correction-factors . 25°C - 1.06 . Cf .
Note. from - 10°C . 0°C . 5°C . 10°C . 20°C . 25°C . 30°C .
Theambient-correction-factor . of Table - A6 is applied to the .earth-fault-loop-impedances . of tables . A1 / A4 if the ambient-temperature is other than . 10°C

GN-3tells us how to do the Calculations .
Ambient-temperature is 25°C . themeasured-earth-fault-loop-impedance . of a circuit-protected by a . 32A type B- circuit-breaker to BS-EN-60898 . should not exceed . 1.16 x 1.06 = 1.23Ω.

GN-3. Do Not Mix up the .ambient-temperature Table . B.2 - 10°C p.121 . Table . B1 - 20°C . p.120
Regulations- 41.3. : ( C ) 6A - 3.83Ω . 10A- 2.30Ω . as you can see . there’s a difference . Yeah
 
TT-Installations . “ Protective-devices “

Disconnection-timeof ( 0.2s ) for TT- installation hasbeen introduced in the . 17[SUP]th[/SUP] Edition . This makes the use of an . RCD orCircuit-breaker with a . residual-element . virtually-essential .

 
UsefulJunk . 2394 :

2008:2011:

Asbefore all Appendices are “ Informative “ other than Appendix 1 . which is “ Normative “ .
Appendix1 is requirement & all others are provided for guidance .

 
2394: Reminder .

By Definition . p.31 . “ Minor-works “
Additions & Alterations to an . installation that do not extendto the . provision of a new-circuit .
 
2394: Reminder . “ Minor-works “
p.31: - Examples . include the . Addition of socket-outlet : or Lighting-pointsto an ( Existing-circuit ) therelocation of a . light-switch . etc .
 
2394: - 559.6.1.9.

Part- 5 : p.178 . A Lighting-installation . shall be appropriate-controlled .
Note : See table - 53.4. p.149 .
Forguidance on the selection of (Suitable-protective . Isolation & Switching-devices)

2394: Can we use . Circuit-breaker - BS-EN-60898 .for Isolation . Functional-switching . Emergency--switching .
BS-EN-60898- Yes . (3) Device is suitable for .on-load-isolation . i.e. disconnectionwhilst carrying . Load-current .
 
UsefulJunk : 41.3.

Maximum( Zs ) for . Circuit-breakers to . BS-EN-60898 - Overcurrent-characteristicsof . RCBO - BS-EN-61009-1 . for. ( Instantaneous-operating ) givencompliance with the . 0.4s & 5s . disconnection-times at . nominal-voltage . (Uo of 230V )

Characteristics- type - B . ( Zs- Ω ) for device of . rated-current . (In ) 46 / In .
Characteristics- type - C . ( Zs- Ω ) for device of . rated-current . (In ) 23 / In .
Characteristics- type - D . ( Zs- Ω ) for device of . rated-current . (In ) 11.5 / In .



 
Circuit-breaker- BS-3871 . Still in Use. Obsolete to BS-7671:2011: standards

Whatis the . Maximum-value of ( Zs ) at anominal-voltage . Uo - 230V .
Type- 2 . circuit-breaker . BS-3871 . with a rated-current ( In -30A ) Maximum-value of ( Zs -230V ) is [ 32.8 / In = 32.86 / 30 = 1.1Ω ]

41.3: - 3A . 6A . 10 .
[ Type - B - right hand side of table - 41.3 ] making me . 46/ In

Your Example to work to . Scenario !!. Type - B. circuit-breaker . rated-current ( In ) of 8A .
Overcurrent- characteristic of . RCBO . Maximum-value of ( Zs ) - 230V is 46 / In = 46 / 8 = 5.75Ω . [ 46 ÷ 8 = 5.75Ω ]





 
Maximum( Zs ) circuit-breakers - BS-3871 . Obsolete to BS-7671:2011: standards
for.( Instantaneous-operating ) givencompliance with the . 0.4s & 5s . disconnection-times at . nominal-voltage . (Uo of 230V )

Type- ( Zs - Ω ) for device of rated-current - ( In )
Type- 1 . 57.5 / In .
Type- 2 . 32.86 / In .
Type- 3 . 23 / In .
Type- 4 . 4.6 / In .

Type- B . 46/ In .
Type- C . 23/ In .
Type- D . 11.5/ In .
 
Example: Basics .

Maximum-Earth-fault-loop-impedance. Overcurrent-protective-device .

(Zs ) can be found using the formula given . in Appendix - 3 - BS-7671: p.295 .Where :- [ Zs = Uo / Ia ]

Uo ) . is the nominal . a.c. - rms .Line-voltage to earth .
Ia) . is the current-causing-operation . of the protective-device within the specified-time. [ 0.4s or 5s ] obtained from the .manufactures-time / current-characteristics. for this particular-device-type & rating .

Example. manufactures-time / current-characteristics . for a 400A - fuse. to BS-88-2 . gives a value of . ( Ia - 2840A ) for a disconnection-time of 5s .
Usingthe above-formula . the maximum-value of ( Zs ) for a disconnection-time - 5s . & a nominal-voltage ( Uo - 230V ) Now - 230V ÷ 2840A = 0.08Ωs .

 
Fig- 3A1 . p.296 . …. it is worth keeping the BS-7671:2008:

Fuses: 2008 : complying with these - withdrawn-standswill be found in . existing installations . for years to come .

BS-1361 is → BS-88-3 : fuse-system C .

Table- 41.2. - ( 0.4s ) BS-88-3 :
Table- 41.4. - ( 5s ) BS-88-3 :

Question. Maximum ( Zs ) value for . BS-88-3 . in 41.4 - (b) How these . maximum ( Zs ) values are obtained.
411.4.5.- Formula - ( Zs x Ia ≤ Uo )

Where:
Zs) . Earth-fault-loop-impedance in Ωs
Ia) . Current in amps . which causes the protective-device to operate . withinthe time-specified in table - 41.1. or
Ifappropriate . within the . 5s . disconnection-time-specified in . regulation -411.3.2.3. for TN-system(s)
Wherean RCD . is used . the current ( Ia ) isthe rated-residual-operating-current . which provides disconnection . within thetime specified in . table - 41.1. . or
Ifappropriate . within the . 5s . disconnection-time-specified in . regulation -411.3.2.3. for TN- system(s)

Uo) . Nominal-voltage to Earth . in Volts- 230V for standard . a.c. Single-phase & Three-phase-circuit(s)
Uo- 2011 ) Nominal . a.c. rms or d.c.line-voltage to Earth in volts - ( V )

Appendix- 3 :
Thevalue of ( Ia ) can be obtained by reference to the appropriate . time /current-characteristic of theprotective-devices & RCDs inAppendix - of BS-7671:2011:

20A- BS-88-3 fuses .
Assumewe have a . 230V - TN - a.c. system with. overcurrent-protection . provided by 20A - BS-88-3 . for a final-circuit - not exceeding 32A .
41.1.- requires that disconnection of the circuit . takes place within a .maximum-time of ( 0.4s )

Youron Calculations .
Maximum-earth-fault-loop-impedance - ( Zs ) which will ensure that . 20A - BS-33 fuses will . disconnect the circuit. within - 0.4s
411.4.5. shown above . but transpose . it to make . ( Uo the subject . this gives ) Uo . Zs ≤ Ia . Uo = 230V .

Toobtain ( Ia ) Fig - 3A1 . Appendix - 3 . time/ current-characteristic . for BS-88-3 . fuses .

Fig- 3A1 . I can’t draw a line .
3A1. representing the . 20A - fuse givesus the value of current . ( 113A ) mucheasier to use the table at the .top-right of the page . fromthis table we can see . that the value of current which causes . 20A - BS-88-3 . fuse to operate within. 0.4s is ( 113A ) back to your formula . ( Uo. Zs ≤ Ia 230V ) Zs ≤ 113 . Zs ≤ 2.04Ω .

Table- 41.2. (b) Maximum - Zs . 20A - BS-88-3. fuse is 2.04Ω

Maximum- ( Zs ) Table(s) & Appendix - 3 . relationship between . the current required to. operate the protective-device . & the earth-loop-impedance-values .



 
Q). 2394 : ( T ) could you get this on Exams.
Documentationfor every electrical-installation . should include that required by . Regulation . ??

p.20. 132.13 .
Everyelectrical-installation . shall be provided with appropriate- documentation .including that required by . Regulation - 514.9. Part - 6 . & where applicable Part - 7 .

 
Q). 2394 : ( T ) could you get this on Exams.
Documentationfor every electrical-installation . should include that required by . Regulation . ?? Sorry .All the Above - 132.13 .
 
2394: Q ) . When automatic-disconnection of supply . is used as a measure of protection. additional-protection by RCD . shall be provided for . ??
Socket-outlets. with a rated-current not exceeding . 20A. that are for the use by . Ordinary-persons & are intended for .general-use. - 411.3.3.
 
2394: Q ) . All circuits in a location .containing a bath or shower shall have . ??
Additional-protectionby . a 30mA - RCD - 701.411.3.3.

Q) . in Exams . this is to warm you up. -&-s
Maximum-disconnection-time. for a lighting-circuit in acommercial-premises . protected by a . TT- system . A) . 0.2s - table - 41.1

Q) . The maximum - ( Zs ) to ensure .30mA RCD operation is . A) . Table - 41.5. 30mA - 1667Ω

Q) . BS-EN-60898 - circuit-breaker can . be used for . Table - 53.2.
Isolation.
Emergency-switching.
Functional-switching.
All of the above

2394: As BS-7671:2011: makes a song & dance about it . “ Line-conductor “ please referto definition
Q) . A Line-conductor includes ?? .
Aconductor of an . a.c. system for the transmission of electrical-energy other than a .neutral . protective-conductors & PEN-conductor . definition

 
Thiswas Posted to me . two-days ago . some reading required .

411.4.5. - Where an RCD is used for . Fault-protectionin a circuit TN-system . the condition ( Zs/ Ia ≤ Uo ) has to be met . just as it does when an. overcurrent-protective-device is used to provide . Fault-Protection . to meetthis condition where an RCD . is used . the earth-fault-loop-impedance ( Zs )in the circuit must not exceed the nominal-voltage of the supply ( Uo ) divided by the current ( Ia )causing-automatic-operation of the RCD within thespecified-maximum-disconnection-time .
Time not exceeding ( 0.4s ) has to beachieved using an RCD to BS-EN-61008-1 & BS-EN-61009-1 . of Non-delay-type. with a rated-operating-current ( IΔn) of 100mA

( a ) in a . circuit of nominal-voltage - 230V . it can be seen from table - 3A . in appendix -3 . BS7671:2011:
That a current of . 100mA is required to cause the RCD to operatewithin - 0.4s . Operation will actually-occur within . 300mS at 100mA .
Accordingly. the maximum-earth-fault-loop-impedance ( Zs ) thatcan be tolerated in the circuit is . 2300Ω - ( 230V ÷ 0.1A = 2300Ω ) …. 100mA ÷ 1000 = 0.1A

RCDs- IΔn - mA

Maximum-valuesof earth-loop-impedance ( Zs - Ω ) for RCDs for fault-protection - TN- systems . operating on 230V .
Earth-loop-impedance ( Zs - Ω ) Circuit-loop-impedance .

Note- ( G - RCDs ) (a)
BS-EN-61008-1:
BS-EN-61009-1: ( 0.4s )
30mA- 7667Ω
100mA - 2300Ω
300mA- 767Ω
500mA- 460Ω

a) . Measured-values of ( Zs) should be lower than those in the above table . as the earth-loop-path in a TN- system is entirelymetallic . The ( Zs - value ) in this table apply to TN- system only .

b) . RCD - time-delay ( S ) Maximum-permitted( Zs ) depends on the rated [ declared-time-delay ] of the RCD .
Todetermine . Maximum - ( Zs ) consultRCD-time-current-characteristics . & obtain ( Ia ) the current inamperes-causing-operation . within the required-disconnection-time-delay ( Zs ) must not exceed ( Uo / Ia )

RCD- time-delayed ( S )
100mA- (b) 0.4s . 1150 Ω .
300mA- (b) 0.4s . 383 Ω .
500mA- (b) 0.4s . 230 Ω .

RCD- time-delayed ( S )
100mA- (b) 5s. 2300Ω .
300mA- (b) 5s. 767Ω .
500mA- (b) 5s. 460Ω .

Forconvenience . it has been listed . the maximum-earth-fault-loop-impedance values( Zs ) for RCDs used for .fault-protection in TN-systems . it is important that the ( Zs) values achieved in the installationshould be much lower . than those given in the table . as the . earth-fault-loop-path. in a TN-system . it should also be noted thatthe . maximum-values of ( Zs ) in theabove relate only to a nominal-voltage of 230V .& should be multiplied by a factor-equal to . Uo / 230V . if othernominal-voltages are to be used .

RCD. is employed for . fault-protection . consideration must also be given to protection against Overcurrent .






 
Usefuljunk . We want the current ( Ib ) to beless than . 10mA - 0.01A “amperes “
mA - milliamp or 1 / 1000 part of an Amp .
 
Backto the past . BS-7671:2001 / 2004 . O.S.G.

1.1.Scope .
Thisguide is for electricians ( Skilled-persons) it covers the following-installations. (in these days you could ask the boss for a pay-rise )

1.1.Scope . 2011 :
Thisguide is for . installers ( forsimplicity , the term installer has been used for electricians& electrical-installers) it covers the following-installations.



 
Usefuljunk

- Ampere or Amps - represents the amount of current in a circuit .
- Voltage- is defined scientifically as . the circuit-potential-difference . & can be seen as the amount of “ Pressure“ that drives electricity in a circuit .
- One-Watt- is equal to one volt . multiplied by one-amp .

Garden-hose.
Thewater-pressure in the hose . is like-voltage
Ampis like the . volume of water-flowing through the hose .
Wattagethen . is the total amount of water that comes out the hose . per unit of time .

Term- that helps tie . together the other three . is the ( Ohm ) which is a unit of ( Electrical-résistance ) going back to the garden-hose . has alarger-diameter . more water will be able to flow through .
- Circuitwith a high-résistance-value . expressed in ( Ωs ) isable to carry fewer-amps . than with lower-résistance . regardless of the voltage.
-High-voltage-encounters-high-résistance . the amount of possible-amps in thecircuit . will be very-low . not muchwater will get through a narrow-hose . no matter how high the pressure is .
 
TT- Installations . “Protective-devices “

Disconnection-timeof ( 0.2s ) for TT- installation has beenintroduced in the . 17[SUP]th[/SUP] Edition . This makes the use of an . RCD or. Circuit-breaker with a . residual-element . virtually-essential .


RCDs- again
TT- installation . the earth-fault-loop-impedance is not usually-sufficiently lowto facilitate the operation of an (Overcurrent-protective-device ) within the required-disconnection-time .BS-7671:2011: as the disconnection-timefor . TT - systems is 0.2s .

TT - systems compared with the ( 0.4s ) required in the Previous-Edition . “how thing have Changed “

TT- installations require attention becausethey normally have a higher-impedance to earth via-an electrode buried in theground . high-earth-fault-impedancewould reduce an . earth-fault-current & slow down the tripping of acircuit-breaker . 2395 : “ RCDs “

Some-Facts: TN- systems have avery-low-earth-impedance . which in most-cases . circuit-breakers would meetrequirements should an earth-fault-occur .
BS-EN-60898 & BS-EN-61099-1- circuit-breakers . designed to trip - 0.1s . reason ( Instantaneously) . requirements for . fault of Low-impedance . between Live-conductors
TT- systems . which have ahigher earth-impedance . they do notreliably meet the requirements for disconnection-time . Backto RCDs again . so . 0.04s / 0.2s

2394: don’t get mixed up on TN- . TT- . Systems . 0.4s - 0.04s / 0.2s - 0.04s . ( If )
TN- low-earth-impedance . ( Zs ) circuit-loop-impedance .
TT- systems . which have ahigher earth-impedance . ( Zs ) circuit-loop-impedance .
 
2394: Where an RCD is used . we have two-methods .
Addition-protection )
Fault-protection )

Wherean RCD is used for ( Fault-protection ) product of the rated-residual-current andthe sum of the resistances of theinstallation - Earth-Electrode . & Protective-conductor (s) connecting it to . exposed-conductive-parts ( R [SUP]A [/SUP]) is required to benot . greater than . 50V - regulation - 411.5.3.

(R [SUP]A [/SUP]) It isrecommended that an . Earth-Electrode-résistance. where possible not-exceed - 200Ω -411.5.3. Note -2

2394: TT - system . do comeinto the Equation . in Exams . ( R [SUP]A [/SUP]) I got this on Exams . 411.5.3. so that there’s no confusion .
P.38 . The sum of the résistance of the . earth-electrode& the protective-conductor .connecting . Etc

Fault-protection: ( ADS ) - TT - system .
TT- system there is no . direct-connection between the installation . MET &the earthed-supply-source - earthed-neutral or star-point . other than throughthe general-mass of the Earth . therefore . particular requirements are necessary- Regulation - 411.5.1.

 
2394:
Dear Customer . RCD / RCBO . Have you tested by . Operation of thepushbutton at . frequent-intervals . Then I can stop using (Grecian-2000 )

Iwas taught to do the ( x5 - test ) first . &if the device didn’t trip . take that as evidence that the ( User )probably wasn’t exercising the device .at the recommended-periods . in thelast six-months I’ve use this method . it can free sticky RCDs . not always , Howdo you get through to your customer . “ RCD is important “
“Seize up “ Lubricant used on the .Latching-mechanism - would emulsify overa period of Time . Yeah . as we wouldsay . “ Push theButton

N****. training-DVD - Inspection & Testing . does say that . Initial-pushbutton testto ( Pre-lubricate the mechanism ) No am not working for the other side .

 
2394 : Known yourregulations .

Earth fault loop impedance (Z[SUB]s[/SUB]) ……. inour case - Circuit-loop-impedance

Regulation612.9 requiresthat, where protective measures are used which require a knowledge of the earthfault loop impedance (Z[SUB]s[/SUB]), the relevantimpedances are to be measured, or determined by an alternative method.
 
Useful junk BS-951

Installing a clamp in an inaccessible position

Likeall types of electrical connection that are not excused by Regulation - 526.3of BS 7671, the electrical connections between a BS 951 clamp, the pipe (or other tube) to which it isattached, and the protective conductor connected to its terminal must beaccessible for inspection, testing and maintenance (Regulation 543.3.3 refers).
Failing to fit a warning label

It is adeparture from Regulation 514.13.1 of BS 7671 to fail toinstall a suitable ‘SAFETY ELECTRICAL CONNECTION - DO NOT REMOVE’ label in avisible position at the connection of an earthing-conductor to an earthelectrode or of a bonding conductor to an extraneous-conductive-part. Such alabel is normally supplied with each BS 951 clamp. Misuse of BS-951 clamps Casesof misuse of BS 951 clamps are occasionally found Fitting a BS-951 clamp to the armour or metallic sheath of a cable BS-951 states that clamps to this standard are notintended for connection to the armour or sheath of a cable and requires thepackaging of the clamp to include the warning “ Notintended for use on the sheath or armour of a cable ”. This is becausethe action of tightening the clamp is liable to damage the cable, for exampleby crushing the bedding or insulation or by causing the metal in a lead sheathto cold-flow. Such damage may result in high resistance and unreliability in theelectrical connection between the clamp and the armouring or metallic sheath,and may even result in an electrical fault within the cable, with thepossibility of serious injury to persons. Fitting a BS951 clamp to the armour or metallic sheath of a cable is thereforeunacceptable. Fitting a BS 951 clamp whichis unsuitable for the pipe diameter and/or cable size.

A BS 951 clamp must be correctly selected for both thesize of pipe or tube to which it is to be fitted and the size of cable. Fittinga clamp which is unsuitable in either of these respects is liable to be adeparture from the requirements of Regulations 526.1 and/or 526.2 of BS 7671 relating to durable electrical continuity,adequate mechanical strength, and appropriate selection of a means ofconnection.
 
2394: As the RCBO . is here to stray . Somefacts . ( i )
Conventional-tripping-current. RCBO-61009-1.

Anovercurrent-protected-pole . is defined by BS-EN-61009-1 . as a pole provided with an overcurrent-release .

Rated-current ( In ) is the maximum-current which an RCBO . isdesigned to carry for long-periods . ata specified-reference air temperature . normallyof 30°C
Theterm ( Rated-current ) generallymeans the same as ( Current-setting ) asused in BS-7671 . in relation to protection against . Overcurrent .

Thepreferred-values of rated-current givenin BS-EN-61009-1 . 6A - In . up to 125A- In . BS -

Rated-residual-operating-current- ( IΔn ) of an RCBO . is the value of . residual-current . assigned to the RCBO by themanufacture . at which an RCBO-operatesunder specified-conditions .

The. Standard-value . of ( rated-residual-operating-current ) BS-EN-61009-1- 0.01A . 0.03A .0.1A . 0.3A . 0.5A .
Re-cap.
10mA ÷ 1000 = 0.01A . . Etc .
500mA ÷ 1000 = 0.5A .

Wherethe function of an . RCBO as a RCD . rather than as anOvercurrent-device . is used for . fault-protection as part of the . protective-measure . ( ADS ) fault-protection depends upon the .RCBOs - sensitivity . as a residual-current-device .

The - Lower the rated- residual-operating-current . the Greater the sensitivity . should the fault be of .non-negligible-impedance . There’s a However .
Ifan RCBO is selected with to . low arated-residual-operating-current . this may result in . unwanted-tripping .

 
2394: As the RCBO . is here to stray . Somefacts . ( ii )

Conventional-tripping-current. RCBO-61009-1.

The conventional-tripping-current . of acircuit-breaker . is the characteristic relating to . protection of the circuitagainst overload . it is a . specified-value of the circuit-current . which causes the device to trip within a specified-time - known as the conventional-time . at the specified-reference-temperature .
Conventional-tripping-current. is usually expressed as a . multiple of the rated - ( nominal ) current - ( In) of the circuit-breaker .

RCBO- residual-current-breakers . conforming to BS-EN-61009-1 . all have a conventional-tripping-current of. ( 1.45 - In ) the related- conventional-time . is
(1 - Hour ) for circuit-breaker(s) of rated-currents ( In ) up to and including ( 63A )
(2 - Hours ) for circuit-breaker(s) of rated-currents . Greater than( 63A )

Symbolgenerally used for . conventional-tripping-current ( I[SUP]2 [/SUP] ) rather than ( I[SUP] t [/SUP] ) as is used in . circuit-breaker standard such as RCBO-61009-1.
This is because . conventional-tripping-current. means the same as the . term .current-causing-effective-operation ofthe . Overload-protective-device . used in - BS-7671 - in which the symbol ( I[SUP]2[/SUP] ) is used .

 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Re-take - Useful Information for 2394 :
Prefix
N/A
Forum
Electrical Course Trainees Only
Start date
Last reply date
Replies
1K

Thread Tags

Advert

Thread statistics

Created
amberleaf,
Last reply from
Richard Burns,
Replies
1,197
Views
29,180

Advert