3 b ) ii) Explain why the earthing conductor is connected to the MET when measuring prospective earth fault current .. 2/M
Ans ; This is the condition that exists at the time of a fault and therefore is the only way to determine the maximum fault current to ( EARTH ) when carrying out the test .
C;
in this case the purpose of the test is to ( Determine ) the maximum prospective earth fault current , This will occur when the installation is energised and all earthing arrangements are in place , so the test must be carried out under these conditions .
3 c) i) List the measurements to be taken , at the main switch of a three-phase TN-S system , in order to determine the installation prospective fault current ( Ipƒ ) .. 3/M
Ans ;
• L1 to L2
• L1 to L3
• L2 to L3
C;
There is no need to carry out any other tests to determine ( PFC ) because on a three-phase system the largest fault current will be due to a symmetrical short circuit , that is a short circuit between all line conductors' at the same time . A test between line conductors is an acceptable approximation . if additional tests were included in the answer then this would not make the answer invalid .
The measurement of , L1 to N , L2 to N and L3 to N would be an acceptable Alternative method see answer to ( 3 c ii below )
3 c ) ii) Explain how the recorded value of prospective fault current ( Ipƒ ) is determined following the test in c) ii) above .. 3/M
Ans ; The highest value of the three measurements
C;
3 c ) i) and ii) are linked and the answer to ii) is dependent on the test method used in i) if the answer to i) was to measure between L & N then this answer would be " the largest value x 2 " if the answer to i) included tests to earth then this answer must state 2 the largest line to neutral value x 2 "
3 b ) ii) Explain why the earthing conductor is connected to the MET when measuring prospective earth fault current .. 2/M
Ans ; This is the condition that exists at the time of a fault and therefore is the only way to determine the maximum fault current to ( EARTH ) when carrying out the test .
C;
in this case the purpose of the test is to ( Determine ) the maximum prospective earth fault current , This will occur when the installation is energised and all earthing arrangements are in place , so the test must be carried out under these conditions .
3 c) i) List the measurements to be taken , at the main switch of a three-phase TN-S system , in order to determine the installation prospective fault current ( Ipƒ ) .. 3/M
Ans ;
• L1 to L2
• L1 to L3
• L2 to L3
C;
There is no need to carry out any other tests to determine ( PFC ) because on a three-phase system the largest fault current will be due to a symmetrical short circuit , that is a short circuit between all line conductors' at the same time . A test between line conductors is an acceptable approximation . if additional tests were included in the answer then this would not make the answer invalid .
The measurement of , L1 to N , L2 to N and L3 to N would be an acceptable Alternative method see answer to ( 3 c ii below )
3 c ) ii) Explain how the recorded value of prospective fault current ( Ipƒ ) is determined following the test in c) ii) above .. 3/M
Ans ; The highest value of the three measurements
C;
3 c ) i) and ii) are linked and the answer to ii) is dependent on the test method used in i) if the answer to i) was to measure between L & N then this answer would be " the largest value x 2 " if the answer to i) included tests to earth then this answer must state 2 the largest line to neutral value x 2 "