I am currently training a electrician and after some advice.

A family member is relocating there kitchen in there house which means they need there cooker supply relocated.

What is the best around this...can it be junctioned rather than running a fresh?

Thanks in advance ...
 
it can be junctioned as long as the junction is capable of carrying the load, and either MF or accessible.
 
Good little job for training. Use these small exercises as a chance for research. All the following regs are relevant to making a jointed cable connection. There are others too.

132.16
133.2.2
513.1
Section 526
Chapter 64
Appx 4 for cable calcs
 
it can be junctioned as long as the junction is capable of carrying the load, and either MF or accessible.

How do I determine this? is there a certain type of junction box I need to use?

What does mf mean?
 
Welcome to the forum mate.

You should apply to join the Trainee Forum section.
People are happier to help out trainees more if they are in this section, and it will also help you out with your "Power to shed" thread.
 
  • Like
Reactions: DPG

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

JayAr91

Trainee
~
Joined
Location
UK
What type of forum member are you?
Trainee Electrician

Thread Information

Title
Relocating cooker supply
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
6

Advert

Thread statistics

Created
JayAr91,
Last reply from
westward10,
Replies
6
Views
1,294

Advert