Hi there im in training, but my question is using using a 3 phase 480v delta to 208/120 delta transformer 30kva and wiring it in reverse for 208 primary input for 480 volt secondary . My motor requirements is 460volts with the motor being 10hp,(14amps) but it has variable motor controls which the calling for the additional 10.5 amps load so total load maximum is 24.5 amps. I know you have to worry about in rush currents and voltage drops. But the motor will only be used 4-6 times a year. AS the 480 primary to 208 is easy to get ordered and delivered but the 208 to 480 6 week lead time. Whats the pros and cons of using it in reverse?
 
Perhaps the main electrical issue is grounding of the secondary side. Since there is no neutral connection to the primary winding, when reversed it will have to be corner-grounded. With one phase grounded, the other two are then at 480V to ground instead of 277V. Additional measures might be needed to ensure code compliance.

Secondly the voltage selector taps will be in the secondary instead of the primary. If your incoming voltage is high, the transformer losses and heat dissipation might be increased because it won't be possible to increase the number of primary turns by changing the tap. However for voltages slightly above nominal this will be offset by the turns ratio compensation.

The compensation will however lower all the output tap voltages, by anything up to twice the percentage regulation. The turns ratio of a step-down transformer is deliberately made less than the nameplate voltage ratio. Off-load it does not quite step down enough, but on-load the copper loss drops the voltage to the correct value. Reverse-feed the transformer and the reduced turns ratio means that the off-load voltage will be low, and the full-load voltage lower.

Finally, and this might be the main issue, is that the manufacturer will probably disclaim all warranty and liability associated with the transformer, if it is not used in accordance with its specification. An inspector would probably side with them, if it were involved in a fire or incident.

Overall might work just fine but there are caveats with both performance and code compliance.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Joined
Location
shreveport , la
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United States of America
What type of forum member are you?
Trainee Electrician

Thread Information

Title
reversing a step down transformer to step transformer
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
1

Advert

Thread statistics

Created
nblender,
Last reply from
Lucien Nunes,
Replies
1
Views
1,016

Advert