I'm a bit confused about the values taken while testing a TT installation. I need enlightening.

Sub main from house 16mm SWA into 4 way CU with 30Ma main switch/RCD.
16mm earthing conductor.

1 ring
1 radial sockets
1 light circuit

Ze = 164 ohms
PFC = 1.4 amps
Zs of ring = 184 ohms

R1+R2 ring 0.34 ohms
R1+R2 radial 0.05 ohms
R1+R2 lights 0.85 ohms

Comments appreciated.
Harry
 
The Zs would usually be less than the Ze and R1+R2 values.(especially, much reduced, if there are parallel earth paths)

Is the rod local to the sub main load end or at the supply side ? (did the testing include the R1+R2 of the SWA) It still would not make up the 20 ohm excess

If not, was this value obtained with an earth loop tester, with the" no trip" function, which is sometimes very inaccurate and therefore ignorable?

Your reading is within recomendations.but there is a question mark against those stated values

The PFC of 1.4 amps ,unless you meant 1400 Amps and forgot the K or you are measuring the prospective earth fault current only
The prospective short circuit current would give a much higher reading than the earth fault current in a TT system
 
The rod is local to the second CU, about 3 metres.

The value was obtaineed with a loop tester with the no trip function on. should i test again with it off?
 
it dosent make a difference mate with the trip on the test just takes a bit longer you should only have it on when doing your zs readings though
 
so apart from the discrepency between the r1r2 and zs compared to the ze reading, everything is ok you think?

on the test results cert, the section which asks for the max Zs permitted by 7671, what value should i put? 1667?

thanks
 
thats fine and you dont have a discrepency on your ring circuit because thats what your reading is .you will not get the same results by calculating zs
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
TT installation queries
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
8
Unsolved
--

Advert

Thread statistics

Created
harrymonkfish,
Last reply from
calv68,
Replies
8
Views
2,065

Advert