Hi,

I'm buying a new test kit and was wondering if anyone had a problem with non trip earth loop readings?

This was taken on the same installation- new mk sentry split load rccb CU.

I've got a secondhand, calibrated megger 1711 MFT which I've taken readings on a ring = 1.04 ohms
And previously tested with a fluke 1662 = 0.54 ohms

Same with cooker radial which calculated res should be 0.31 (ze + r1 + r2.) And thr megger read 0.72 ohms!

And the readings are consistent like this on all circuits. No good for me if I'm doing lots of EICRs.

Now I've read that some people experience 0.5 ohm uplift with rcds but I've never had anything this high before!

I need a reliable test kit asap! What are your experiences with these testers, and what would people recommend?

Thanks

Dan
 
megger MFTs are generally good on no trip Zs testing. less prone to noise than flukes. maybe try and compare readings with a mate's megger, of check yours for calibration.
 
megger MFTs are generally good on no trip Zs testing. less prone to noise than flukes. maybe try and compare readings with a mate's megger, of check yours for calibration.
Hi,
Thanks for the reply.
You can lose/gain ohms with badly connecting test leads.
The tester itself could be calibrated fine.
That did cross my kind, but I made sure I was on securely and repeated tests 4 times and got all the same readings?
 
possiblecause... on the megger, you don't have to null the leads for Zs. i think that on the fluke, you do. this could be the cause.
 
I think if I got the readings you originally got and the latter ones I would suspect there is a bad connection/s somewhere on the ring and would have to look around a bit to check if that is true. On the basis of your figures you must have a ring circuit that is very large, can't be bothered to work it out. Have you done the calcs prior to testing that would show what they should be based on the length (estimate) of the circuit?
 
An error of 0.5 ohm is not outside of the "RCD uplift" figure that you see mentioned.

I suspect that any new MFT are OK for doing reasonably accurate no-trip measurements. My DiLOG 9118 seems to give sane results in both high current and no-trip testing, and in keeping with DC measurements of R1+R2. Sadly not earth rod testing (beyond doing a Ze on it).
 

Reply to High no trip earth loop readings in the Electrical Tools and Products area at ElectriciansForums.net

Similar Threads

Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
Gents. I did some earth loop tests on Rolec power pedestals (2x 16 amp outlets) that are harbour side, looped in and out from one another. Three...
Replies
7
Views
2K
I've managed to mainly fix a Megger 1502 MFT that was so far out of calibration it got laughed out of a tester day. I have high current loop. rcd...
Replies
11
Views
2K
Morning, Customer has a intermittent trip which I am trying to locate. 4 circuits on rcd. Two rings , cooker and hob and one I cannot find...
Replies
4
Views
3K
My main tester is a Megger MFT1711, which I bought second hand but came with a calibration certificate. Rather than annual calibration, I have a...
Replies
4
Views
3K

Electricians Tools | Electrical Tools and Products

Thanks for visiting ElectriciansForums.net, we hope you find the Electricians Tools you're looking for. It's free to sign up to and post a question yourself to find a tool or tool supplier either local to you, or online. Our community of electricians and electrical engineers will do their best to find the best tool supplier for you.

We also have a Tiling Tools advice from the worlds largest Tiling community. And then the Plumbers Forums with Plumbers Tools Advice.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock