Hi
I've never posted in one of these forums before, but have read lots of threads and found them extremely helpful.
So it makes sense seeing as I know the knowledge on this sight is very impressive to ask you guys for help.
I have a problem with a job and can't work out what the problem is I've been back there two days in a team of two and haven't fixed the problem and I'm starting to feel a bit stupid :)
It all started when I got a call from a customer I completed a full rewire and extension for last year, She claimed to be getting small shocks from the metal light switches in one room of the house. I turned up expecting it to be something simple, Maybe even static.
Turns out at that switch there was 44v on the earth wire.
Ok so at this point I'm thinking that some where on the circuit there is a damaged cable, not enough to trip but slight damage
I strongly suspect that the most likely cause is a plate screw slightly intruding on the insulation of a live so I unscrew all the plates.
I should add at this point that I went to the fuse board in the garage and discovered that they had a new automatic garage door fitted and the rails ran right in front of the fuse board, Giving me just enough space to get the fuse board cover off but not to safely work in it or test properly.
However back to the point I discovered that every earth on a feed in or out cable has voltage on it some as high as 100v!. When I turn the breaker off to this circuit this voltage disappears completely.
I disconnect the earth of this circuit out of the board and this earth has voltage, So its not coming from the mains, This is where it gets confusing to me, I disconnect all the earths from each other and from the board expecting to find which cable has the fault. All the earths are still live!
This doesn't seem possible to me and I'm hoping someone will make me feel stupid and point out something I've missed
I'm assuming the neutrals must be involved because otherwise it wouldn't be possible for all earths to be live even when disconnected from each other.
As a temporary solution I have removed all the metal plates and replaced them with plastic. Obviously the customer is not happy with this and I need to go back and remove the garage door bracket to get to the board and test properly.
Any replies of help would be most welcome (I'm a desperate man) please feel free to make me feel stupid I have no doubt in my ability as an electrician but I am also under no illusions that there are electricians which have forgotten more than I know! Seriously though I really appreciate you taking the time to read this and would appreciate ALL suggestions, I really want to sort this because how else do we learn
I would start by confirming voltages between L&N L&E and N&E both at the incomer and then on the final circuits.
There's a few things I don't fully understand from your post, especially the part about separating the earths and the neutrals being involved.
A few questions first;
Did you test the incoming supply?
What is the earth impedance of the supply?
I can give you some general advice, if you get ashock from something then there at least two faults present. Firstly there's an insulation problem causing current to leak down the CPC to earth. Secondly there's an earthing problem which allows a high touch voltage to develop because the earth impedance is too high.
Tracing this problem by measuring the touch voltage isn't the best way, rather use your mega tester to find the low insulation fault and then use your earth impedance tester to find the earthing issue.
You have mentioned an automatic garage door has been fitted since you rewired, I would start looking in that area first. The people who fitted it may have only been garage door fitters "cus it's only free wires innit, wot cun goo rong."
if you are getting a voltage N-E with your CU main switch off, i'd strongly suspect a fault on the supply. need Ze readings for a start, then IR tests on the installation. could there be a problem with a neighbour's installation back feeding your earth?
Lots of questions to answer so please let me know if I miss any
first of all let me clarify that if I remove the cpc for this circuit from the earthing terminal in the consumer unit I still have voltage on all the earths including the disconnected one in the consumer unit but not from the main earth bar.
secondly I then disconnect all the cpc's from each other at each switch (fed at switches not 3 plate) I still have voltage on the earth on the incoming and outgoing feed even though they are disconnected from each other
The initial verification test was mainly performed by myself however dead tests were done by someone else and I did the final test in a two man team
i have spoken to the second man and he has admitted to me that he tried to take an earth loop but the tester wouldn't let him so he worked it out from the R1 + R2
the the earth impedance of the supply is recorded as 0.05
the garage door is just on a plug top plug into the garage ring
i think I've covered it all?
Oh dear!, so instead of investigating this issue (above 50V touch ?), the installation was put into service with a possible inherent defect.
Oh and to clarify as well when I switch off the breaker to this circuit only the earth voltage disappears
so, the stray voltage must be coming from that MCB. dis all that circuit's cables from CU. do continuity and then IR tests on that circuit with all loads disconnected. bet you the IR tests will show a L-E fault on that circuit.
Reply to Voltage up to 100v on CPC even when disconnected in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Hi everyone, When checking my consumer unit voltages with the full board off, I stumbled across something head scratching. Measuring the feed...
Old two core cable in a lighting circuit with no cpc at any point All points had metal fixtures and fittings class1 At two points the live loop...
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Hello All and happy new year. Over the holiay I have changed all of my old sockets to some nice new ones and added a couple with usb sockets for...