Can wago 773 connectors be used on a ringmain? As they are rated at 24amps and i cant find a definitive answer
 
In theory yes, as each leg of a 32A RFC should be capable of carrying 20A.
Depends on other issues too though, conductor size/enclosure/location etc and is so are they MF rated
 
  • Like
Reactions: Jase222
In theory yes, as each leg of a 32A RFC should be capable of carrying 20A.
Depends on other issues too though, conductor size/enclosure/location etc and is so are they MF rated
Thanks, just found there's a wago 773 @ 41amps which I have just ordered
Cheers
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Bristol
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Trainee Electrician

Thread Information

Title
wago 773
Prefix
UK 
Forum
UK Electrical Forum
Start date
Last reply date
Replies
2

Advert

Thread statistics

Created
Jase222,
Last reply from
Jase222,
Replies
2
Views
997

Advert