Discuss What are the possible causes of low IR readings at 500VDC? in the UK Electrical Forum area at ElectriciansForums.net
Bizron
Kitchen RFC 2.5 T+E - IR=>200MOhms at 250VDC L&N to E but 0.34MOhms at 500VDC L&N to E.
I suspect damp/corrosion in sockets, what do you reckon?
All socket switches opened including SFCU to cooker hood, F/F, D/W and W/M.
Damp issues would be evident at 250v, as above surge protected lead or surge protection within an appliance. It could be an rcd spur or socket however these normally indicate low readings even at 250v.
Thanks for replies, I am trying to get an idea of actual readings for different accessories/appliances that can point me in the correct direction of what to hunt for. Today I was in a hoarders house with access to every socket impossible, got low readings LN&E, fridges/freezers always seem to have some leakage that will skew readings.
Reply to What are the possible causes of low IR readings at 500VDC? in the UK Electrical Forum area at ElectriciansForums.net
Slightly strange one this, replaced a few socket fronts in a dining room today, all wiring original but new plasterboard on a studded wall. Its a...
I have been carrying out an EICR on a property and have come across this black tarry substance on 2 of the cables. I have seen the pitch oozing...
4K
Looking for some guidance here. I'm currently shadowing a guy and we're testing a new extension on a school. 3 phase TNCS supply from the original...
Hi,guys went to do an EICR and when doing IR test I got L-E ON RFC like 0.02 MOHM and two lighting circuits L-E AND L-N the results were like 0,14...
What are the dangers of poor insulation resistance results (i.e <1Mohm) between neutral and earth? If all other tests are ok, what are the...
5K