Hi all. Changing a CU in an ex-council flat, pme system, no RCD's, and initially tried to IR test whole board L/N joined to earth, got a reading of 0.28 Ohms.

Then did each circuit individually (2 X RFC, 2 X lights, 1 X cooker), L/N joined to the circuit's CPC, and got between 0.25 and 0.30 Ohms on each one.

Any ideas what could be causing the low readings?

Thanks.
 
always get that with PME. it's because the N bar is tied to earth at the service head with bonding to services contributing.
 
With the main switch OFF? When you tested the circuits individually, did you remove the N's from the bar? If not, each test was still a global test, and an N-E fault on one circuit will show up on all.
 
Then did each circuit individually (2 X RFC, 2 X lights, 1 X cooker), L/N joined to the circuit's CPC, and got between 0.25 and 0.30 Ohms on each one.
Assuming the individual N was out during each test that is odd. Having a N-E fault on every circuit is a bit more than coincidence and more like an installation with some serious flaws!
 
if the 0.3 ohms reading per circuit is correct a global 0.06 ohms would be a global reading drawing 3.833 KW .either measurement errors , SPDs or item still in circuit (possibly wired incorrectly ) is there an RCD present?
 
Sorry, my mistake - I meant MegaOhms, not Ohms.

No RCDs, no SPDs and an empty property so I couldn't even find anything plugged in. I did the individual tests removing L, N and CPC from the board, so that's why I can't understand why they all had pretty much the same low reading. Wiring is singles in conduit, but can't see how that can make a difference.

It seems there is a problem but I can't even think what that problem might be!
 

Reply to Insulation resistance whole board. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
646
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
709
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
I'm writing this mainly hoping something occurs to me while writing it! I got called to an occasionally tripping RCD. It's a Hager double height...
Replies
19
Views
2K
Over the last few days, I have stumbled across a number of threads that seem to point to a prevalent misunderstanding. Either that, or I have been...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock