Hi all. Changing a CU in an ex-council flat, pme system, no RCD's, and initially tried to IR test whole board L/N joined to earth, got a reading of 0.28 Ohms.

Then did each circuit individually (2 X RFC, 2 X lights, 1 X cooker), L/N joined to the circuit's CPC, and got between 0.25 and 0.30 Ohms on each one.

Any ideas what could be causing the low readings?

Thanks.
 
always get that with PME. it's because the N bar is tied to earth at the service head with bonding to services contributing.
 
  • Like
Reactions: Wilko
With the main switch OFF? When you tested the circuits individually, did you remove the N's from the bar? If not, each test was still a global test, and an N-E fault on one circuit will show up on all.
 
Then did each circuit individually (2 X RFC, 2 X lights, 1 X cooker), L/N joined to the circuit's CPC, and got between 0.25 and 0.30 Ohms on each one
did you disconnect from the board or tails in the board .
 
How are you reading ohms on an IR test ? Is it not MegaOhms ?
 
Assuming it has a DP main switch which was off, most likely some circuit has a N-E fault and as they are common on the N bar you see the global test fail.

Need to pull each N out in turn to find it.

If it were L-E a MCB would have found it dam quick!
 
Then did each circuit individually (2 X RFC, 2 X lights, 1 X cooker), L/N joined to the circuit's CPC, and got between 0.25 and 0.30 Ohms on each one.
Assuming the individual N was out during each test that is odd. Having a N-E fault on every circuit is a bit more than coincidence and more like an installation with some serious flaws!
 
  • Like
Reactions: DPG
if the 0.3 ohms reading per circuit is correct a global 0.06 ohms would be a global reading drawing 3.833 KW .either measurement errors , SPDs or item still in circuit (possibly wired incorrectly ) is there an RCD present?
 
Sorry, my mistake - I meant MegaOhms, not Ohms.

No RCDs, no SPDs and an empty property so I couldn't even find anything plugged in. I did the individual tests removing L, N and CPC from the board, so that's why I can't understand why they all had pretty much the same low reading. Wiring is singles in conduit, but can't see how that can make a difference.

It seems there is a problem but I can't even think what that problem might be!
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined

Thread Information

Title
Insulation resistance whole board.
Prefix
UK 
Forum
UK Electrical Forum
Start date
Last reply date
Replies
9

Advert

Thread statistics

Created
Bobble23,
Last reply from
Bobble23,
Replies
9
Views
2,793

Advert