M
Mr_Freeze
Hi Everyone,
I moved into a new build house 1 year ago.
I’ve got round to investigating the supply to my separated garage.
At the house the builders have fitted a fused spur (non switched) internally onto a ring circuit fused at 13amp.
From this is a short length of 2.5 T&E going externally to a plastic Ip66 mounted external JB.
From this a 1.5 SWA is run underground to the garage and terminated into a metal clad switched fused spur inside the garage.
A double socket is connected to the spur on the incoming side.
The lighting circuit is connected to the load side and the fuse is 5amp. The switched spur therefore acts as the light switch.
The SWA has an earth conductor but the armourings are not earthed separately in the plastic JB. No banjo is fitted at the metal clad spur but the back box is bonded to the earth core.
Questions on existing instal.
Should the internal spur have a switch providing DP isolation before it leaves the house?
Should the armourings be earthed by bonded banjos to the earth core at both ends?
Planned changes.
I would like to replace the metal clad switched spur with a new garage CU with a main isolator with RCD and 2 x MCB’s fitted. 6amp for lighting and 10amp for sockets.
I then plan to wire multiple sockets around the garage in plastic conduit with LNE singles.
Would there be any issues in doing this as in my mind I’m providing DP isolation in the garage with RCD protection and separate rated MCB’s for lights and sockets?
Appreciate any comments?
Planned changes.