G
Geoff101
We’ve had a few power glitches/cuts recently by our supplier. Each time, on power restoration our RCD has tripped. Irritatingly we were on holiday when it happened last - not good for frozen food!
When we had an extension 3 years ago some changes were made to the consumer unit and a new RCD was fitted into it. This was done by a qualified electrician with all the tests etc carried out. Since then I've never just been able to reset the RCD when tripped - I've always needed to switch all the MCBs off, reset the RCD and then reset the MCBs one by one.
I've now done some investigation trying to reset the RCD with just one of the MCBs in the on position and it appears that almost any individual circuit will prevent the RCD resetting if the MCB is left on.
We don't generally have any problems with other nuisance RCD trips - once it's reset everything is fine.
I haven't been round to remove everything that is plugged in, and some of the circuits that prevent resetting are lighting circuits anyway. I did try one experiment as an example - The oven circuit MCB, if on, prevented the RCD resetting. This circuit only has the oven connected to it. With the oven isolator switched off but the MCB on it allowed the RCD to reset - so clearly not an issue with the circuit itself. Switch the oven isolator on again and the RCD couldn't be reset. It's a fairly new built-in AEG dual oven and am pretty confident it's not faulty.
So the big question is, does this sound like it could be a faulty RCD which doesn't like being reset with any sort of load on it? In the case of the oven it obviously wasn't actually on and heating, just in standby with the electronics active. I'm guessing whatever earth leakage surge there is on power up is triggering the RCD - as it appears is happening in most the other circuits. Interestingly though, using the oven as an example the 'surge' is enough to prevent the RCD being reset, but clearly not enough to trigger it once reset and the MCB is put on.
I don't know how common it is for the RCD to be suspect like this - and if faulty it appears it has been from the start. Worth a swap to see?
Thank for any thoughts....
The cumulative leakage of the circuit may be close to the trip value of the RCD (this will be less than 30mA in practice). May be worth getting a spark to check the leakage with a sensitive clamp meter.
Reactions: DMElec.1
I agree it could be a factor. However, of the 10 circuits on the CU, 8 of the 10 each individually prevent the RCD resetting when only their MCB is on. Surely if it was cumulative thing, if each was leaking enough to trigger it individually then with all switched on there would be no hope of the holding even when reset? Or have I got it wrong?
What kind of neutral issue? A short would tend to cause tripping when load is highest, not when circuits are energised with minimal load on. High resistance would cause malfunction of the loads and/or overheating of faulty terminations etc.
The OP's systematic investigation and findings make suspect the RCD, and it is worth testing with an RCD tester or by substitution, along with the key electrical parameters of the installation. Many people assume their RCD is faulty for all sorts of spurious reasons, for which the cause usually turns out to be one of a number of standard problems such as an N-E short or aggregate leakage near threshold. None of those seem to fit here.
If the RCD is good, the only likely external influence is the presence of devices that create a leakage impulse when first energised. This can occur with suppression capacitors inside appliances etc. but then the behaviour would likely be specific to one or two circuits. One thing I would check first, if it has not already been checked, is the supply polarity. If all the MCBs are switching the neutral, the leakage transients from operation will be abnormal. Obviously this is also a dangerous situation as the MCBs will not offer fault protection to earth and single-pole functional switching will leave points live.
One way or another, electrical test equipment now needs to be brought to bear on the installation and I will be interested to hear the outcome.
Hi - do you know what earthing system you're using at home - do you have a rod in the garden for example?
Hi
Thanks for all your thoughts - really helpful.
For a bit more background the house is a 30s extended semi and I guess was rewired in the 80s. We didn’t have this problem until 3 years ago when the kitchen was extended and some circuits were added/changed. A couple of spare ways in the existing mk sentry CU were used and a new RCD was fitted. The new and altered circuits were tested and I have the test cert from this. The issue of having to switch off the MCBs to reset the rcd was there from this point on. Never been a particular problem until recently as we have had quite a run of power outages and realised the consequences if we are away when it happens. On reflection, some circuits were unaltered by this work, with the old rcd in it used to reset fine with the MCBs on but this is no longer the case. These circuits may have been moved on the cu but nothing more than that. This makes me wonder even more if it is the new rcd which is the culprit.
I’m guessing there is a earth rod in the garden but I’m not entirely sure about that. We have had a new supply cable fitted from road to house within the last year as when they came to fit a smart meter they discovered bitumin leaking from the old cable and replaced it, the meter and head, main fuse. So everything on the supply side of the cu is new. And hasn’t changed anything.
The polarity is correct and the MCBs are indeed switching the live!
I wish there was an isolator so I could try a substitute rcd but there’s not.
I think I’ll need to get someone in but I would hopethey might start with a quick substitution as I’m feeling this could be a quick win..... or maybe not!
Oops... my mention of polarity there was irrelevant as I was thinking about a problem you don't have (trip events when operating the MCBs).
The way forward is definitely electrical testing but I can't resist speculating. There's a scenario where both the RCD and the installation test OK, but a new RCD solves it, e.g a faulty RCD contact that arcs under the stray capacitive load of the wiring as it is being manually reset, but makes adequate contact once fully closed. In that case it would still pass ordinary RCD tests. As the installing electrician should have done these with all loads disconnected, it could have been faulty from new but wouldn't necessarily have misbehaved during commissioning.
Yes, Lucien, I think that perfectly describes my thoughts. Once set, everything works ok. We don’t have any spurious RCD trips under normal operations, but the RCD definitely works (I’ve occasionally N E tripped it when changing light fittings etc).
It’s definitely the actually resetting action that is the problem.
My plan is to see if I can get the spark who did the work for us last time to swap the rcd and see if that does it. If not I’ll ask him to investigate futher.......
  • Optimistic
Reactions: buzzlightyear
Would a N E fault not keep the rcd tripped all the time? Why would it only trip when trying to reset and not once reset and why would switching the MCBs off then allow it to reset?
Not saying it wouldn’t I just need the thoeory explained to me....
When you reset the RCD with MCBS on, all the appliances you have plugged in are all trying to come on at the same time.
Have you tried unplugged everything and having the MCB's on when resetting?
Is it an RCD, or an RCBO/RCCB. And what is its current rating? (overload?) (photograph of consumer unit would help)
The combined load of everything starting up may be tripping the breaker side
had this a few times on older installations.1 or 2. 2 MCBs on, RCD would not reset. all MCBs off, reset RCD, turn MCBs on 1 at a time.
Reactions: Dave OCD
Yes but some circuits are lighting circuits with the lights all off, the oven circuit just had an oven on which surely shouldn’t trigger it one it’s own otherwise everyone would have the problem.
It’s an MK rcd 7880s. 80a 30ma.
What was there before the new rcd was fitted? Was it a straight forward main switch?
I've come across the problem a few times over the years where the RCD (If I recall always a 4293 not a 61008) will only reset with all mcb's off. My recollection is it has invariably been a N-E fault, I cant remember having to change an RCD to rectify the problem. That said it's been a while and my memories not what it was......
No, it used to have an rcd but I think it was changed when the work was done. Could it have had a wider rcd which was changed for a narrower one to open up more ways on the board?
I recall we needed addional ways and I think this is how it might have been achieved without changing the cu. make sense or not?
Yes that’s possible with that fuseboard although if your electrician has changed that rcd, it doesn’t comply with regulations.
There are regulations regarding discrimination which your installation falls short of. He/ she should not have issues certs staying that it complies.
However, getting back to the troubles at hand, it may be prudent to unplug everything within the house, leave the mcb’s on and then try and reset the rcd just to see if it’s an appliance or a number of appliances causing the issue. The start up of a lot of things at once may cause an issue.
Just trying to narrow it down!
If you eliminate the impossible, then all that remains, however improbable, must be the truth!
Alas and alack, simply opening a single-pole mcb does not disconnect the neutral wiring. So, with any but only one mcb turned on and then closing the double pole RCD all the final circuits line and neutral circuitry are in play as far as electrons are concerned including current paths to earth and especially transient currents as these circuits are made live but not energised to full mains(240V) potential - apart from the circuit of the closed mcb.
My simple experiment would be to disconnect the L, N and cpc of the induction hob circuit at the CU ; it's my number one suspect for your problem because of its in-line power EMI filters and how they respond to transient voltages between L and N and L and E and N and E. Then, with all mcbs closed try re-energising the board - I suspect the problem will go away. Put the induction hob on its own rcbo. If not I think you will find a number of mcbs can now be closed and then energised. Final circuits which might give you a problem will have white goods, microwaves and some types of computer equipment which use the earth/cpc for EMI filtering purposes.
Herein lies a problem - the sole RCD is also the Main Switch. What needs to be arranged is a Main Switch which supplies the RCBO for IH and the RCD for all the remaining mcbs. I don't think you have room fit an a new Main Switch and an new RCBO unless one combines some final circuits. If it was me I would replace the CU with a Main Switch and dual RCD board plus RCBO for IH or plump for the top end aka Murdoch solution - Main Switch and all RCBOs for final circuits.
(Please take a photo of your cut out, earthing bar and meter arrangements so we can try and discover the earthing system in use.)
Good post from Marconi.
And from now on the all RCBO board will be known as the 'Murdoch Solution'. Brill.
Yeh Macaroni’s posts are always full of big long technical words. Unlike some. Eh Buzz:p
Hopefully you can find the culprit.
Turn off the power. Do all the street lights outside go off too?
  • Funny
Reactions: Dave OCD and DPG
Thanks. Really helpful. I’ll try that tomorrow when I get time.
In terms of following your advice for the future set up and keeping things as simple as possible would it be in order to add a main switch which then fed the existing consumer unit and also split to feed a new unit with single RCBO to feed the IH. Obviously then moving the IH circuit from the old CU and leaving a spare way?
Prob not the neatest way of doing it but would it meet requirements?
You also have a standard bonding clamp connecting your main earth to the cable sheath. This is not acceptable as a means of connection and can be dangerous as it will compress the cable. Do not disturb it, and contact your supplier to arrange for a proper clamp to be installed.
Picking up on Wirey's thought - I hope there is a connection back up to the Consumer Unit somehow. I could be totally incorrect, but I see the 2 conductors going down (to gas and water perhaps) but none coming up with the meter tails. Is there one in that trunking perhaps?
Following my previous post maybe something like this and consider moving both the IH and oven on this with RCBOs in it?
I Wylex NM206/63 | 2 Way Consumer Unit | Fast UK Delivery | Buy Now - https://www.electricpoint.com/wylex-nm206-63-2-way-63a-main-switch-metal-consumer-unit.html?utm_source=googlebase&utm_medium=datafeed&utm_campaign=google-shopping&gclid=Cj0KCQiAxNnfBRDwARIsAJlH29DCxq2ooi0EIAXSIGX2hcWs2gkE2dsm1F58XDREtFkBLCZmw_lrIOkaAnITEALw_wcB
Interesting. This was fitted by the supplier about 4 months ago.....!
It’s in the trunking....
Ooooh, is that a 'smart meter' I see before me?
There's a recent thread along a similar line of RCDs tripping in proximity to SMs.
Is there any correlation here?
Interesting! It’s always tripped on reset but only recently has been tripping at other times. I thought this correlated to power interruptions but can’t be sure on all of them. The smart meter has only been there a few months so there is a possible connection..... how to tell though.....?!
What does that sticker say? £5 fine for cutting the seals?
I think I can live with that.
Thanks for this - I've now tried this theory, sadly with no success - but may lead uis nearer a diagnosis possibly....
I tried switching off both the IH and oven. They are both on DP isolators so this will have fully removed both their L and N from the circuits. With them removed both the RCD would properly reset with their MCBs on. (they both have their own individual circuits with nothing else connected). However, in both cases, when the isolator was put on again the RCD would not reset for either circuit unless the MCB was off. Also, as before with the oven and IH isolated none of the other circuits in the house would allow an RCD reset unless the MCB was off.
Which I guess for me is again swinging me back to asking the question, do I have a faulty RCD as any sort of a live load on it appears to prevent a reset action but once reset it appears to work fine?
This changes the diagnosis quite significantly. If there have been random trip events while energised, then any or all possible types of fault need to be considered, such as N-E shorts. Further speculation is futile until we have IR measurements and RCD test results etc.
Reactions: marconi
Although I can’t be 100%, the times it has tripped when we have been around has been related to power outages. They’ve recently been working on power cables in the street and this is when it has started. It has tripped twice when we’ve not been here and will I can’t be sure I’m pretty certain it will have been a power glitch which then tripped in re engergisation which is the part I guess I am reproducing.
It clearly could be n e fault but I’m still thinking if it were a permanent n e problem it would stay tripped and not reset at all. If it was an intermittent n e fault then it would be tripping randomly and also letting me reset it via the rcd. ????
them smart meters are the invention of the devil. just as bad as google earth being able to see what's going on in my bedroom at night. blast it with a 12 bore. see what supplier thinks of that.
Re Geoff101 #32: Thank you for reporting back. I think it does take us forward. I reread your opening post and thought about the changes to the MK Sentry CU when you had your extension works - you said 'a new RCD' was fitted - by which I think you mean the original switch disconnector (Main Switch) was replaced by a combined RCD and Switch Connector from the MK78xxs series - this would neatly fit in the space vacated by the Main Switch.
Then I studied the picture of you CU - which is the old set up of Main Switch on the right - nowadays they are on the left - I think it has been standardised to be so. There is a consequence then to simply swapping the MS for the RCD and having the line mcb busbar to the left: it means that the L and N meter tails to the RCD enter to the left and right respectively which is NOT what MK intends for the MK78xxs RCD (and indeed for most other brands). Why? Because like modern switched sockets the neutral contacts are arranged to close first and open last - that aint going to happen in your CU. The line contact is made first and then the neutral afterwards. This will play havoc with the transient potential differences between the installations Line to Earth conductors and Neutral to Earth conductors. So, as I said in one of my earlier emails, in earthed neutral systems switching should be such that the neutral is made live first (by connecting to the supply N) and then the installation Line made live and energised to mains potential.
So, your installation's RCD I believe is satisfactory - but needs to proven to be so nevertheless - it is simply responding to the reversed order of Line and Neutral RCD switching and the effect this has on brief transient leakage currents through L-cpc and N-cpc of the final circuits . By turning off all the mcbs (and the oven, cooker, IK isolators) and then resetting the RCD the final circuits are not being energised to mains potential until the RCD L and N contacts have completed making. Then once final circuits have their neutrals referenced to earth potential through low conductance paths the closing of their mcb and energisation does not cause a residual current problem the RCD cannot tolerate. Simply put for a given final circuit all the wiring of it leaps to 240V with respect to earth and then the neutral side drops to neutral/earth potential. When correctly switched, only the line side leaps to 240V. Much more transient leakage occurs in the former case than the latter.
So, I reckon this is a possible reason why the replacement of the Main Switch for an RCD/Disconnector has inadvertently introduced the problem you describe. The solution is to arrange for the correct order of switching of L and N by the RCD.
Hi Marconi, I think you might have cracked it!
It did previously have an rcd. Not sure if the exact model but I recall it was 4 modules wide similar to this pictured.
Rather than change the cu when we needed extra ways for the extension I remember the spark telling me he was changing the rcd to a later version to free up extra ways which is logical. By changing to the 7880 we had 2 extra ways for MCBs. However the diagram on the old one pictured does appear to show the live on the left where as the current one shows it on the right. As you point out, that would explain why it functions perfectly once reset but struggles to reset with any load. Thanks!
The next question of course is how to solve it in a simple way! I’ve attached a pic showing the inside of the current cu.
1) simple but fear not likely is does anyone know of an rcd of this size that has the live on the left? Even in a past model? Then I could do a straight swap.
2) I assume that this rcd can be put on the left and I can shuffle the MCBs along to the right to make space. However, that obviously requires moving the neutral bus to the left with it which looks fun, and whether there is enough neutral cable on all the circuits to do this is debatable.
3) I could obviously go the whole hog and put a completely new cu in.
4) I guess a slightly bodged approach would be to replace the rcd with a plain isolating switch and put a stand alone rcd in the tails before the consumer unit. Seems messy but would it meet requirements?
What would you do?!
Any ideas greatfully received!
A further query I’ve just thought of....
The initial problem with prompted this was the rcd sometimes tripping after a power interruption. Would this recevrsed layout lead to this or not. Once the rcd is actually switched is there any difference in terms of whether it’s l and n are reversed? In this case it’s not actually switching as it is already on. Will reversal affect it’s proper operation?
If not then is it possible that we’ve just been unlucky in that the last few power cuts have been accompanied but some sort of surge no reconnection which has tripped the rcd?
I certainly know that one was accompanied by a significant surge as it killed a wireless thermostat and a heated towel rail timer in one go!
Geoff ,a BG 80a/30ma RCD is arranged with the neutral on the right, they are also reasonably priced and I've never had an issue with them. However this is just for information as I'm not condoning fitting different makes of device in a CU, the regs frown upon it. :eek::rolleyes:
Can't reset the RCD with any MCB's on - Faulty RCD?
Geoff101,
Bul,