Alas and alack, simply opening a single-pole mcb does not disconnect the neutral wiring. So, with any but only one mcb turned on and then closing the double pole RCD all the final circuits line and neutral circuitry are in play as far as electrons are concerned including current paths to earth and especially transient currents as these circuits are made live but not energised to full mains(240V) potential - apart from the circuit of the closed mcb.

My simple experiment would be to disconnect the L, N and cpc of the induction hob circuit at the CU ; it's my number one suspect for your problem because of its in-line power EMI filters and how they respond to transient voltages between L and N and L and E and N and E. Then, with all mcbs closed try re-energising the board - I suspect the problem will go away. Put the induction hob on its own rcbo. If not I think you will find a number of mcbs can now be closed and then energised. Final circuits which might give you a problem will have white goods, microwaves and some types of computer equipment which use the earth/cpc for EMI filtering purposes.

Herein lies a problem - the sole RCD is also the Main Switch. What needs to be arranged is a Main Switch which supplies the RCBO for IH and the RCD for all the remaining mcbs. I don't think you have room fit an a new Main Switch and an new RCBO unless one combines some final circuits. If it was me I would replace the CU with a Main Switch and dual RCD board plus RCBO for IH or plump for the top end aka Murdoch solution - Main Switch and all RCBOs for final circuits.

(Please take a photo of your cut out, earthing bar and meter arrangements so we can try and discover the earthing system in use.)

Thanks. Really helpful. I’ll try that tomorrow when I get time.
In terms of following your advice for the future set up and keeping things as simple as possible would it be in order to add a main switch which then fed the existing consumer unit and also split to feed a new unit with single RCBO to feed the IH. Obviously then moving the IH circuit from the old CU and leaving a spare way?
Prob not the neatest way of doing it but would it meet requirements?

C3DCAE01-0012-4EA0-BE74-56C2C11EE1D0.jpeg


167FEE6D-D40F-45AB-A74D-77D805FF946B.jpeg
 
You also have a standard bonding clamp connecting your main earth to the cable sheath. This is not acceptable as a means of connection and can be dangerous as it will compress the cable. Do not disturb it, and contact your supplier to arrange for a proper clamp to be installed.
 
Picking up on Wirey's thought - I hope there is a connection back up to the Consumer Unit somehow. I could be totally incorrect, but I see the 2 conductors going down (to gas and water perhaps) but none coming up with the meter tails. Is there one in that trunking perhaps?
 
Thanks. Really helpful. I’ll try that tomorrow when I get time.
In terms of following your advice for the future set up and keeping things as simple as possible would it be in order to add a main switch which then fed the existing consumer unit and also split to feed a new unit with single RCBO to feed the IH. Obviously then moving the IH circuit from the old CU and leaving a spare way?
Prob not the neatest way of doing it but would it meet requirements?

View attachment 45909

View attachment 45910

Following my previous post maybe something like this and consider moving both the IH and oven on this with RCBOs in it?

I Wylex NM206/63 | 2 Way Consumer Unit | Fast UK Delivery | Buy Now - https://www.electricpoint.com/wylex-nm206-63-2-way-63a-main-switch-metal-consumer-unit.html?utm_source=googlebase&utm_medium=datafeed&utm_campaign=google-shopping&gclid=Cj0KCQiAxNnfBRDwARIsAJlH29DCxq2ooi0EIAXSIGX2hcWs2gkE2dsm1F58XDREtFkBLCZmw_lrIOkaAnITEALw_wcB
 
You also have a standard bonding clamp connecting your main earth to the cable sheath. This is not acceptable as a means of connection and can be dangerous as it will compress the cable. Do not disturb it, and contact your supplier to arrange for a proper clamp to be installed.

Interesting. This was fitted by the supplier about 4 months ago.....!
 
Ooooh, is that a 'smart meter' I see before me?
There's a recent thread along a similar line of RCDs tripping in proximity to SMs.
Is there any correlation here?
 
Ooooh, is that a 'smart meter' I see before me?
There's a recent thread along a similar line of RCDs tripping in proximity to SMs.
Is there any correlation here?

Interesting! It’s always tripped on reset but only recently has been tripping at other times. I thought this correlated to power interruptions but can’t be sure on all of them. The smart meter has only been there a few months so there is a possible connection..... how to tell though.....?!
 
Alas and alack, simply opening a single-pole mcb does not disconnect the neutral wiring. So, with any but only one mcb turned on and then closing the double pole RCD all the final circuits line and neutral circuitry are in play as far as electrons are concerned including current paths to earth and especially transient currents as these circuits are made live but not energised to full mains(240V) potential - apart from the circuit of the closed mcb.

My simple experiment would be to disconnect the L, N and cpc of the induction hob circuit at the CU ; it's my number one suspect for your problem because of its in-line power EMI filters and how they respond to transient voltages between L and N and L and E and N and E. Then, with all mcbs closed try re-energising the board - I suspect the problem will go away. Put the induction hob on its own rcbo. If not I think you will find a number of mcbs can now be closed and then energised. Final circuits which might give you a problem will have white goods, microwaves and some types of computer equipment which use the earth/cpc for EMI filtering purposes.

Herein lies a problem - the sole RCD is also the Main Switch. What needs to be arranged is a Main Switch which supplies the RCBO for IH and the RCD for all the remaining mcbs. I don't think you have room fit an a new Main Switch and an new RCBO unless one combines some final circuits. If it was me I would replace the CU with a Main Switch and dual RCD board plus RCBO for IH or plump for the top end aka Murdoch solution - Main Switch and all RCBOs for final circuits.

(Please take a photo of your cut out, earthing bar and meter arrangements so we can try and discover the earthing system in use.)

Thanks for this - I've now tried this theory, sadly with no success - but may lead uis nearer a diagnosis possibly....

I tried switching off both the IH and oven. They are both on DP isolators so this will have fully removed both their L and N from the circuits. With them removed both the RCD would properly reset with their MCBs on. (they both have their own individual circuits with nothing else connected). However, in both cases, when the isolator was put on again the RCD would not reset for either circuit unless the MCB was off. Also, as before with the oven and IH isolated none of the other circuits in the house would allow an RCD reset unless the MCB was off.

Which I guess for me is again swinging me back to asking the question, do I have a faulty RCD as any sort of a live load on it appears to prevent a reset action but once reset it appears to work fine?
 
Alas and alack, simply opening a single-pole mcb does not disconnect the neutral wiring. So, with any but only one mcb turned on and then closing the double pole RCD all the final circuits line and neutral circuitry are in play as far as electrons are concerned including current paths to earth and especially transient currents as these circuits are made live but not energised to full mains(240V) potential - apart from the circuit of the closed mcb.

My simple experiment would be to disconnect the L, N and cpc of the induction hob circuit at the CU ; it's my number one suspect for your problem because of its in-line power EMI filters and how they respond to transient voltages between L and N and L and E and N and E. Then, with all mcbs closed try re-energising the board - I suspect the problem will go away. Put the induction hob on its own rcbo. If not I think you will find a number of mcbs can now be closed and then energised. Final circuits which might give you a problem will have white goods, microwaves and some types of computer equipment which use the earth/cpc for EMI filtering purposes.

Herein lies a problem - the sole RCD is also the Main Switch. What needs to be arranged is a Main Switch which supplies the RCBO for IH and the RCD for all the remaining mcbs. I don't think you have room fit an a new Main Switch and an new RCBO unless one combines some final circuits. If it was me I would replace the CU with a Main Switch and dual RCD board plus RCBO for IH or plump for the top end aka Murdoch solution - Main Switch and all RCBOs for final circuits.

(Please take a photo of your cut out, earthing bar and meter arrangements so we can try and discover the earthing system in use.)

Thanks for this - I've now tried this theory, sadly with no success - but may lead uis nearer a diagnosis possibly....

I tried switching off both the IH and oven. They are both on DP isolators so this will have fully removed both their L and N from the circuits. With them removed both the RCD would properly reset with their MCBs on. (they both have their own individual circuits with nothing else connected). However, in both cases, when the isolator was put on again the RCD would not reset for either circuit unless the MCB was off. Also, as before with the oven and IH isolated none of the other circuits in the house would allow an RCD reset unless the MCB was off.

Which I guess for me is again swinging me back to asking the question, do I have a faulty RCD as any sort of a live load on it appears to prevent a reset action but once reset it appears to work fine?
 
I thought this correlated to power interruptions but can’t be sure on all of them.

This changes the diagnosis quite significantly. If there have been random trip events while energised, then any or all possible types of fault need to be considered, such as N-E shorts. Further speculation is futile until we have IR measurements and RCD test results etc.
 
This changes the diagnosis quite significantly. If there have been random trip events while energised, then any or all possible types of fault need to be considered, such as N-E shorts. Further speculation is futile until we have IR measurements and RCD test results etc.

Although I can’t be 100%, the times it has tripped when we have been around has been related to power outages. They’ve recently been working on power cables in the street and this is when it has started. It has tripped twice when we’ve not been here and will I can’t be sure I’m pretty certain it will have been a power glitch which then tripped in re engergisation which is the part I guess I am reproducing.
It clearly could be n e fault but I’m still thinking if it were a permanent n e problem it would stay tripped and not reset at all. If it was an intermittent n e fault then it would be tripping randomly and also letting me reset it via the rcd. ????
 
them smart meters are the invention of the devil. just as bad as google earth being able to see what's going on in my bedroom at night. blast it with a 12 bore. see what supplier thinks of that.
 
Re Geoff101 #32: Thank you for reporting back. I think it does take us forward. I reread your opening post and thought about the changes to the MK Sentry CU when you had your extension works - you said 'a new RCD' was fitted - by which I think you mean the original switch disconnector (Main Switch) was replaced by a combined RCD and Switch Connector from the MK78xxs series - this would neatly fit in the space vacated by the Main Switch.

Then I studied the picture of you CU - which is the old set up of Main Switch on the right - nowadays they are on the left - I think it has been standardised to be so. There is a consequence then to simply swapping the MS for the RCD and having the line mcb busbar to the left: it means that the L and N meter tails to the RCD enter to the left and right respectively which is NOT what MK intends for the MK78xxs RCD (and indeed for most other brands). Why? Because like modern switched sockets the neutral contacts are arranged to close first and open last - that aint going to happen in your CU. The line contact is made first and then the neutral afterwards. This will play havoc with the transient potential differences between the installations Line to Earth conductors and Neutral to Earth conductors. So, as I said in one of my earlier emails, in earthed neutral systems switching should be such that the neutral is made live first (by connecting to the supply N) and then the installation Line made live and energised to mains potential.

So, your installation's RCD I believe is satisfactory - but needs to proven to be so nevertheless - it is simply responding to the reversed order of Line and Neutral RCD switching and the effect this has on brief transient leakage currents through L-cpc and N-cpc of the final circuits . By turning off all the mcbs (and the oven, cooker, IK isolators) and then resetting the RCD the final circuits are not being energised to mains potential until the RCD L and N contacts have completed making. Then once final circuits have their neutrals referenced to earth potential through low conductance paths the closing of their mcb and energisation does not cause a residual current problem the RCD cannot tolerate. Simply put for a given final circuit all the wiring of it leaps to 240V with respect to earth and then the neutral side drops to neutral/earth potential. When correctly switched, only the line side leaps to 240V. Much more transient leakage occurs in the former case than the latter.

So, I reckon this is a possible reason why the replacement of the Main Switch for an RCD/Disconnector has inadvertently introduced the problem you describe. The solution is to arrange for the correct order of switching of L and N by the RCD.
 

Attachments

  • MK142-0610Aen_DOWNLOAD[1].pdf
    7.7 MB · Views: 11
Last edited:
Hi Marconi, I think you might have cracked it!
It did previously have an rcd. Not sure if the exact model but I recall it was 4 modules wide similar to this pictured.
Rather than change the cu when we needed extra ways for the extension I remember the spark telling me he was changing the rcd to a later version to free up extra ways which is logical. By changing to the 7880 we had 2 extra ways for MCBs. However the diagram on the old one pictured does appear to show the live on the left where as the current one shows it on the right. As you point out, that would explain why it functions perfectly once reset but struggles to reset with any load. Thanks!
The next question of course is how to solve it in a simple way! I’ve attached a pic showing the inside of the current cu.
1) simple but fear not likely is does anyone know of an rcd of this size that has the live on the left? Even in a past model? Then I could do a straight swap.
2) I assume that this rcd can be put on the left and I can shuffle the MCBs along to the right to make space. However, that obviously requires moving the neutral bus to the left with it which looks fun, and whether there is enough neutral cable on all the circuits to do this is debatable.
3) I could obviously go the whole hog and put a completely new cu in.
4) I guess a slightly bodged approach would be to replace the rcd with a plain isolating switch and put a stand alone rcd in the tails before the consumer unit. Seems messy but would it meet requirements?

What would you do?!

Any ideas greatfully received!

F10901F5-0FF9-43F9-B31D-0B184231072F.jpeg


B62178FE-1F91-473B-A14B-DDC3B5293069.jpeg
 
A further query I’ve just thought of....
The initial problem with prompted this was the rcd sometimes tripping after a power interruption. Would this recevrsed layout lead to this or not. Once the rcd is actually switched is there any difference in terms of whether it’s l and n are reversed? In this case it’s not actually switching as it is already on. Will reversal affect it’s proper operation?
If not then is it possible that we’ve just been unlucky in that the last few power cuts have been accompanied but some sort of surge no reconnection which has tripped the rcd?
I certainly know that one was accompanied by a significant surge as it killed a wireless thermostat and a heated towel rail timer in one go!
 
Geoff ,a BG 80a/30ma RCD is arranged with the neutral on the right, they are also reasonably priced and I've never had an issue with them. However this is just for information as I'm not condoning fitting different makes of device in a CU, the regs frown upon it. :eek::rolleyes:
 

Reply to Can't reset the RCD with any MCB's on - Faulty RCD? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi I am asking for help as a novice and 1st time user of this forum. Recently started to experience tripping of MCB & sometimes with the RCD at...
Replies
7
Views
539
Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
1K
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
321
Hi, I seem to have an RCD that keeps cutting the power at random times without actually tripping, if I reset it, the power comes on and will stay...
Replies
7
Views
449

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock